0 members (), 164 guests, and 10 robots.
#23907 03/30/03 01:28 PM
I have 2 old spools of THW wire. Is is permissible to use this anymore?
I am thinking about using it feed a tool shed through 3/4 pvc.
If not, I will be taking a run to the scrap yard.
Thanks,
Peter
Peter
#23908 03/30/03 01:35 PM
It is listed in 310.13 as OK for dry and wet locations, there is no reason not to use it.
Remember if you run out more than 1 circuit you will need a ground rod out there.
#23909 03/30/03 01:41 PM
Thanks Bob. It's for a single circuit, so I don't have to worry about the ground rod.
Peter
#23910 03/30/03 05:41 PM
Ron Offline
THW is a great conductor as its insulation is more durable (thicker) during a pull through conduit. It is rated for wet environment, as underground installation must be considered.
[This message has been edited by Ron (edited 03-30-2003).]
Ron
#23911 03/30/03 05:43 PM
Doesn't "THW" signify THermoplastic, Wet location?
#23912 03/30/03 08:13 PM
The H in THW probably designates it as 75°C insulation, versus TW being 60°C. In a number of areas, it was the default industrial building wire before THWN/THHN was popular. Earlier, THW aced out RHW with improved ease of handling.
[No hepcat electrician would use solid TW if he could get stranded THW.] At one time, TW was available in solid up to 6AWG.
[This message has been edited by Bjarney (edited 03-30-2003).]
#23913 03/31/03 01:25 PM
K
"THW----PVC insulated building wire. Flame-retardant, moisture and heat-resistant, 75deg C. Dry and wet locations."
From Essex Wire&Cable Reference Guide 1997.