20/20 panels 24/40 panels--I have an idea of what this is all about, but would love to hear your clarification of panels. A 20/20 can handle 20 circuits, with 20 breakers only. Please .............join in
|
|
|
|
Joined: May 2001
Posts: 552
Member
|
A 20/20 panel can use only 20 full size breakers.A 20/40 can use 20 full size,40 minis or any combination in between.You are not to exceed the 40 breaker maximum by adding piggyback style breakers.
[This message has been edited by txsparky (edited 03-25-2003).]
Donnie
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
The way I understand it: 20/20 means that the panel is built & listed for 20 branch circuit poles. (20 single poles or 10 double poles, or any combo to 20) This also indicates that "full size breakers are "only" allowed in this panel.
24/40 means 24 full size breakers (24 poles) or by installing listed "twins" or "piggy back" a maximum of 40 poles. The panel buss is supposed to be manufactured with a means to prevent the insertion of "twins" in excess of the "listed" quantity.
John
John
|
|
|
|
Joined: Jan 2003
Posts: 1,429
Member
|
How about C-H Panel 100Amp 30 space has anyone used this panel.
|
|
|