#23053 03/10/03 04:42 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
We want to protect an insulated #6 THHN with 1/2" EMT instead of PVC. Will running an insulated ground wire through EMT choke the current if it does return on that wire? I know if it is bare, EMT should not be used.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#23054 03/10/03 05:55 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
If this is a grounding electrode conductor, it must be bonded to the EMT at both ends. See 250.92(A)(3)

If this is an equipment ground, generally speaking, it has no business being run outside of the raceway or cable that contain the circuit conductors.


Few things are harder to put up with than the annoyance of a good example.
#23055 03/11/03 09:54 AM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
Thanks Tom,
The insulated #6 is for a jumper that will go from a satellite dish grounding conductor to the building electrode. To tie the two grounds together for article 810.21(J) Its one of those ground items that does not come up very often, but we want to do it to code.