ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 262 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#222128 03/08/23 09:05 AM
Joined: Apr 2002
Posts: 203
T
triple Offline OP
Member
My contention is that a steam humidifier (Carel model UE015XWOU1) can be considered a continuous load. This model is listed at 11.25 kw, 31.2 amps, 208 volts, three phase. 125% of 31.26 amps (figured from kw rating) is 39 amps. The inspector is allowing this load to be carried by an existing set of 10 thhn wires (35 amps in the 75 degree column). This is even neglecting the overfilled-with-16-C.C.C. pipe (50% derating) that these wires arrive in from the panel. Any comments?

Work Gear for Electricians and the Trades

Workgear for Electricians

triple #222129 03/08/23 09:49 AM
Joined: Apr 2002
Posts: 203
T
triple Offline OP
Member
BTW, I neglected to add: 50% of 40 amps (90 degree column) results in only 20 amps

triple #222131 03/08/23 01:11 PM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
My guess is '#10 at 35 amps, (didn't think continuous) nameplate says 31.2; OK'

May not have seen # of conductors in branch circuits conduit.

BTW, what is/was the outcome??


John

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5