#221933 09/22/22 12:25 PM
Joined: Feb 2010
Posts: 7
S
New Member
Having trouble with Siemens plug on neutral GFCI CIRCUIT BREAKERS. These are tripping as soon as I connect any load, even my LED work light. My supply house & several Chief Inspectors are telling me there are no reported problems, but other contractors are telling me they change them out after inspections( I don't like that solution). 1 inspector suggested changing brands which means changing my primary supplier. All input would be appreciated.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Jul 2004
Posts: 10,056
Likes: 40
G
Member
Is this one circuit or several circuits. This can be caused by a down stream neutral to ground connection. That tends to happen in those over stuffed ceiling boxes as often as anything. You can't get all the neutrals under a big wirenut without some copper showing and it gets grounded.
As soon as you put a load on it, some of the current is diverted to ground and trips the GFCI. A regular breaker doesn't see anything wrong. They also don't like multiwire circuits but that usually needs 2 loads, one on each ungrounded conductor to make it trip.


Greg Fretwell

Link Copied to Clipboard