#221631 10/29/21 11:48 PM
Joined: Mar 2005
Posts: 240
Member
Ok, I am struggling to find the answer to minimum wire size allowed to be encased in concrete. My situation is a parking lot light with with #6 AWG encased in the concrete from the ground rod…I see that #4 is the minimum for rebar connection i.e. ufer, but does that apply to this ground rod? I feel like since #6 needs physical protection, it would also need physical protection coming up the sauna tube and out of the concrete pad for the light pole, however my foreman disagrees and is using #6 instead of # 4 regardless of my input regarding physical protection for # 6.

Thoughts???

As always thanks for all you guys do and the great combined experiences/knowledge of our trade.

H20

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
250.64(B)(3) allows you to just let the #6 to stick up out of the concrete but as an installer I would stub it up in a dollar's worth of RNC. The chance of it surviving until they set the pole is better. #4 might be better if it was tied to the steel and there was no visqueen under the slab but you still can't legally call it a ufer.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,291
Joined: December 2000
Top Posters(30 Days)
BigB 4
triple 3
Popular Topics(Views)
303,134 Are you busy
232,158 Re: Forum
216,886 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5