ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Using THWN on automotive circuits
by BigB - 03/23/23 11:19 AM
Continuous load
by HotLine1 - 03/08/23 02:11 PM
How's all our Non-US folks doing?
by dsk - 03/08/23 11:56 AM
Old Computers?
by Bill Addiss - 03/04/23 05:06 PM
New in the Gallery:
Burger King crown sillyness
Burger King crown sillyness
by wa2ise, December 11
240/208 to a house
240/208 to a house
by wa2ise, October 9
Who's Online Now
0 members (), 55 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Apr 2020
Posts: 1
S
New Member
I have a big commercial grow operation coming up that's going to need an electrical service larger than 1200A, and 1200A is the largest size I've ever designed and installed. I don't even know what the next size would be. Is there a 1600A and a 2000A? If so I've never heard of them.

Let me know your thoughts on this subject please.

Joined: Jul 2004
Posts: 9,796
Likes: 15
G
Member
When they get that big, you usually have engineering support. Standard breaker sizes in article 240 are 1600 2000 2500 3000 4000
5000 6000 but there are bigger ones. I suppose you could dig out all the answers you need from the NEC but I have always been looking at engineered drawings when I see anything much over 800 amps. It was only a few times inspecting but in computer center design, 1600a or 2000a services were not unusual before computers got small.


Greg Fretwell
Joined: Apr 2002
Posts: 7,336
Likes: 7
Member
From a few states to the east of you...
Larger than 1200 amp services are not uncommon here. First off, you should check with the local POCO to determine their restrictions on capacity at your requested voltage.

Our local POCO requires plans and specs before they will come out for a pre-con site meeting.

Here you would be required to submit plans, specs, cut sheets, and load calcs from a Licensed Design Professional, signed and sealed.

For instance, a 1.8M sq ft fulfilment center that requested 2x8000 amp, 277/480 volt services wound up doing primary 13.2KV with ALL equipment past the 13.2 KV feeder being customer owned and installed. That is except the metering equipment (PT/CTs).

4000 amp, 277/480 are the max our POCO can provide under "Normal" conditions.

If I were you, I would start with the POCO, after I prepared a preliminary load calc.


John

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,035 Are you busy
233,456 Re: Forum
218,144 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5