Hello- I have a question about installing mc cable under a patio or porch that is 12 x 12 open wall.
I say damp location.
Are stamped octagon boxes and screw type connectors allowed?
Thank you
Don't drive and TEXT! Drive now TALK LATER!
|
|
|
|
Joined: Jul 2004
Posts: 10,001 Likes: 35
Member
|
If it is a rain tight deck, (no water feeds through the cracks) it may be damp but I would still use bell boxes. Those galvanized octagon boxes will still rust up pretty bad in a damp location. I am not sure how they are listed because few people even try it here.
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,406 Likes: 7
Member
|
Although the Code allows MC, I will go along with where Greg is going regarding the patio/deck being rain tight.
Are you talking alum jacket MC, or steel jacket? Personally I would have an issue with alum jacket being 'outside'. Note I say 'personally'. Or are you talking PVC jacketed MC which would be no issues, with the listed connectors, and a suitable box for the enviornment.
Maybe PVC conduit and PVC device boxes would be a better choice?
John
|
|
|
|
Joined: Jul 2004
Posts: 10,001 Likes: 35
Member
|
There was a while when aluminum MC cable was sold as wet location. I am not sure why it was OK and then why it wasn't.
Greg Fretwell
|
|
|
|
Joined: Jul 2004
Posts: 10,001 Likes: 35
Member
|
I like RNC but it does have that sagging problem in the summer unless you strap it every 2 feet or so and you also need to deal with expansion issues.
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,406 Likes: 7
Member
|
Greg:
I take that label as the rating/listing for the conductors, not the jacket, unless I'm missing something here.
I have seen the al jacket corroding in a few unfinished (older) basements that had no cliamate control.
John
|
|
|
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,438
Joined: February 2004
|
|
|
|
|