1 members (Scott35),
524
guests, and
23
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Sep 2019
Posts: 21 Likes: 1
OP
Member
|
Hi all, I'm new here, first post. I'm taking my Minnesota Master exam this month and wanted a resource to ask some questions that are causing me hair loss <:
I'm having trouble with this question, any direction would be appreciated.
"Equipment grounding on a cord and plug connection has to be shorter then the neutral pin for safety." True or False
Seems simple enough but I can not find a code reference to this answer. Here's where I have looked (NEC2017): 250.114 250.124(A) 250.130(A) 250.138 590.4(D)(1) 590.6(B)(3) 406.4(C) Internet research: 250.24(C) Article 200 210.4(B) 300.13(B)
I'm thinking the answer is False as the over current protection device determines the disconnection and therefore safety, but I'm uncertain how to prove this using the code.
Thanks all, Phil
Where ever you go, there you are.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Welcome pcsailor!
False, check 250.124(A)
Has to be longer for first -make last-break connections
Bill
Last edited by Bill Addiss; 09/04/19 10:00 AM. Reason: added last part
Bill
|
|
|
|
Joined: Sep 2019
Posts: 21 Likes: 1
OP
Member
|
Wow, tough one for me. I read that to but didn't get my head around it. Thanks Bill 😁 Phil
Where ever you go, there you are.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Glad to help Phil,
Bill
|
|
|
|
Joined: Sep 2019
Posts: 21 Likes: 1
OP
Member
|
Hi, I want to dive a bit deeper into 250.124(A) (NEC2017) Here is the actual code: "(A) Separable Connections. Separable connections such as those provided in drawout equipment or attachment plugs and mating connectors and receptacles shall provide for first-make, last-break of the equipment grounding conductor. First-make, last-break shall not be required where interlocked equipment, plugs, receptacles, and connectors preclude energization without grounding continuity."
Here's the question, and answer, from my course practice test: "Equipment grounding on a cord and plug connection has to be shorter than the neutral pin for safety." Answer: "No 250.124.A"
Am I correct in understanding the code language that this answer of 'No' (or False) is specifically referring to the second sentence of 250.124(A)? If so, how do 'cord and plug connections' 'preclude energization without grounding continuity'? I mean, we could be talking about simple extension cords here, yes? You can cut off the ground terminal and the two ungrounded conductors still have an electrical path when plugged in.
What am I missing?
Thanks, Phil
Where ever you go, there you are.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Phil, "Equipment grounding on a cord and plug connection has to be shorter then the neutral pin for safety." True or False Here's my take on it: False Refers to: Separable connections such as those provided in drawout equipment or attachment plugs and mating connectors and receptacles shall provide for first-make, last-break of the equipment grounding conductor. To do that the Grounding Pin is longer. First-make, last-break shall not be required where interlocked equipment, plugs, receptacles, and connectors preclude energization without grounding continuity. This part is just saying it doesn't have to be longer, doesn't say it must be shorter than Neutral or nonexistent. So, still False
Bill
|
|
|
|
Joined: Sep 2019
Posts: 21 Likes: 1
OP
Member
|
Thanks.
Confusing wording in this code section.
Phil
Where ever you go, there you are.
|
|
|
Posts: 43