220.4A and 300.3B applied to neutral bar mounted i #220153 07/29/19 05:08 PM
Joined: Jan 2014
Posts: 7
M
mgawat Offline OP
New Member
220.4A and 300.3B applied to neutral bar mounted in overhead wireway.
First of, let me start by saying I am not young. I may have been lead into some possibly non complying practices over the last 50 YEARS which is WHY i ASK QUESTIONS.
The SCENARIO IS A 480/277V PANELBOARD WITH 3 2" CONDUITS EXTENDING VERTiCALLY ABOUT 40" into a A 10 X 10 X 48" WIREWAY WHICH is attached up tight to the finish ceiling. Now, in the past, we always considered that assembly as one big panelboard and once the cable conductors entered that wireway, one could pretty much do what one wants with them...i,e, install a grounding bar in the wireway to run all the branch circuit grounding conductors and so the same thing with an isolated neutral bar which saves counts on the conductor fill of the 40" 2' pipe to minimize conductor derating.

I have been doing it this way for well over 20 years until today when I was inspected by the senior state of Maine electrical Inspector. He states that 220.4A and 300.3b prohibit doing that and all the individual neutral conductors associated with each branch circuit must go all the way to the grounded terminal in the main feeder panel.

Does anyone smart out there have an opinion on this?. At one time, the State of Maine electrician's examaining board had issued an adoption stating that they would consider all electrical equipment on the same backboard as the feeder panel part of that FEEDER PANEL AND ONE COULD INSTALL THE NEUTRAL BAR WHEREVER ONE WISHED AS IT WAS NOW IN THE PANELBOARD ASSEMBLY.[

Last edited by mgawat; 07/29/19 05:09 PM.
2017 / 2014 NEC & Related Books and Study Guides
Re: 220.4A and 300.3B applied to neutral bar mounted i [Re: mgawat] #220155 07/30/19 10:16 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
The Inspector is right.
Be happy that you got away with a misinterpretation for over 20 years before you got caught.


Ghost307
Re: 220.4A and 300.3B applied to neutral bar mounted i [Re: mgawat] #220156 07/30/19 06:24 PM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline
Member
I suppose 300.4(B)(4) could lead to this confusion but it does not appear that this condition applies. (2017)

Quote
(4) Column-Width Panelboard Enclosures. Where an auxiliary
gutter runs between a column-width panelboard and a pull
box, and the pull box includes neutral terminations, the
neutral conductors of circuits supplied from the panelboard
shall be permitted to originate in the pull box.


Greg Fretwell
Re: 220.4A and 300.3B applied to neutral bar mounted i [Re: mgawat] #220167 08/01/19 01:19 PM
Joined: Apr 2002
Posts: 7,122
HotLine1 Online Content
Member
The column width panels that I have seen over the years (few & far between) have had a neutral bar in the pull box section that was supplied with the panelboard as a complete unit. ie: 'Factory supplied' with documentation regarding the size of the neutral conductor stated.

As I said, few and far inbetween.


John
Re: 220.4A and 300.3B applied to neutral bar mounted i [Re: mgawat] #220172 08/04/19 12:49 PM
Joined: Jan 2014
Posts: 7
M
mgawat Offline OP
New Member
the adoption of 220.4 (b) IN THE 2011 nec CODE pretty much says I can't sdo that any longer but I still don't understand the concern especially with non-metallic conduits running between the panelboard and the metallic wireway 40" away.

Re: 220.4A and 300.3B applied to neutral bar mounted i [Re: mgawat] #220174 08/04/19 03:11 PM
Joined: Jan 2018
Posts: 7
L
libellis Offline
New Member
A bit confused. The last time there was an Article 220.4 in the NEC was in the 2002 edition. In 2005 NEC articles in 220 were renumbered and 220.4 became 220.18. In any case, the old 220.4 and present 220.18 address maximum loads.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 5
NORCAL 1
Popular Topics(Views)
260,712 Are you busy
195,744 Re: Forum
185,132 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3