Water heater calculationsSo when I count calculati #220021 04/11/19 07:23 PM
Joined: Mar 2005
Posts: 235
watersparkfalls Offline OP
Member
My question is I have a 250 gallon Water heater do I calculate at 100% or 125%? This is branch circuit not feeder calculations. Thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Water heater calculationsSo when I count calculati [Re: watersparkfalls] #220022 04/11/19 07:30 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
That's a big tank.
Is this for a locker room with showers?


Ghost307
Re: Water heater calculationsSo when I count calculati [Re: watersparkfalls] #220023 04/11/19 07:32 PM
Joined: Mar 2005
Posts: 235
watersparkfalls Offline OP
Member
OK I see article 422.10 says 125% but where is the code reference to the breaker size one size higher? My water heater is listed at 87 A so 90 A is next standard breaker size.

Re: Water heater calculationsSo when I count calculati [Re: watersparkfalls] #220024 04/11/19 07:46 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
You need to take 125% of the full load current; so it needs to be treated as a 108.75A load.
Make sure to also upsize the wire accordingly.


Ghost307
Re: Water heater calculationsSo when I count calculati [Re: ghost307] #220027 04/13/19 12:42 PM
Joined: Mar 2005
Posts: 235
watersparkfalls Offline OP
Member
Thanks, ghost.
H20

Re: Water heater calculationsSo when I count calculati [Re: ghost307] #220028 04/13/19 12:43 PM
Joined: Mar 2005
Posts: 235
watersparkfalls Offline OP
Member
Yeah exactly gym inside google bldg.
H20


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
267,162 Are you busy
201,870 Re: Forum
190,464 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3