Conduit fill Calculations #219842 12/08/18 08:37 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline OP
Member
1-1/4 in EMT #1 THHN Table C4 allows 4 conductors. This exceeds the 40% fill limit per Table 1 Why is this allowed?


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Conduit fill Calculations [Re: George Little] #219843 12/08/18 09:39 PM
Joined: Jul 2004
Posts: 9,409
G
gfretwell Online Content
Member
Dunno, when I run it I get 1.59 sq in and a 1.25 EMT is 1.50
Didn't someone just tell me NFPA was infallible wink


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,745 Are you busy
195,070 Re: Forum
184,480 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3