1-1/4 in EMT #1 THHN Table C4 allows 4 conductors. This exceeds the 40% fill limit per Table 1 Why is this allowed?


George Little
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2004
Posts: 9,677
Likes: 9
G
Member
Dunno, when I run it I get 1.59 sq in and a 1.25 EMT is 1.50
Didn't someone just tell me NFPA was infallible wink


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Top Posters(30 Days)
NORCAL 3
Robski 1
Popular Topics(Views)
287,962 Are you busy
220,093 Re: Forum
206,091 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5