ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
2 circuit track lighting all of a sudden cross con
by gfretwell - 11/18/19 11:55 PM
Look at this mess...
by NORCAL - 11/15/19 10:21 PM
Fire source!
by sabrown - 11/07/19 08:39 AM
Parallel Conductor Divisor
by LongRunner - 11/04/19 02:21 AM
FPE in Germany
by Texas_Ranger - 10/29/19 05:12 AM
New in the Gallery:
FPE Breaker panel in germany
What is this for?
Who's Online Now
1 registered members (HotLine1), 4 guests, and 15 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Am I the last guy who noticed ... #219661 09/28/18 02:22 PM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline OP
Member
... when they moved good old table 310.16 that has been around since electricity that they changed the ampacity of 14ga and 12ga in the 60c column? (Table 310.15(B)(16) now)

Or am I just missing something?
It is insignificant in regular branch circuits because of 240.4(D) but that will affect motor circuits.
I am a bit ashamed it took me 4 years to see that (the 14 was actually only adopted here this year) but I am retired and not looking at this every day.


Greg Fretwell
2017 / 2014 NEC & Related Books and Study Guides
Re: Am I the last guy who noticed ... [Re: gfretwell] #219663 09/29/18 04:49 PM
Joined: Jan 2018
Posts: 7
L
libellis Offline
New Member
Changes were made in the 2011 NEC. Found the following explanation (extracted from a longer article about the 2011 changes).


"The ampacity of some conductors in Table 310.15(B)(16) (formerly 310.16) didn’t match those found in the Canadian Electrical Code and were therefore changed. While no technical evidence was submitted showing insulation failure of the conductors, this proposal was passed. The end result was a change to the ampacities of:

Copper conductors: 14, 12, 3, and 1 AWG, and 600kcmil, 1,500kcmil and 2,000kcmil.

Aluminum conductors: 12, 8, and 6 AWG, and 300kcmil, 700kcmil, and 800kcmil."

Re: Am I the last guy who noticed ... [Re: gfretwell] #219664 09/29/18 10:54 PM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline OP
Member
I am really surprised I didn't hear much about that. It certainly changes the answer to that question on the inspector test about a 120v 1HP motor with 14ga wire.


Greg Fretwell
Re: Am I the last guy who noticed ... [Re: gfretwell] #219675 10/01/18 05:18 PM
Joined: Apr 2002
Posts: 7,122
HotLine1 Online Content
Member
Greg:

No, you are not alone on this. I just ‘discovered’ this today. (Frown)


John
Re: Am I the last guy who noticed ... [Re: gfretwell] #219682 10/01/18 09:53 PM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline OP
Member
Like I say, this certainly throws a monkey wrench into what you can do in motor circuits. I keep thinking there is an exception I haven't found. I got my CEUs online 4 years ago based on the 11 code and I do not remember this being brought up. I did know 310.16 was moved but I never heard it was changed. That is the problem with being retired. I am not really paying that much attention these days. I didn't even renew my license last year so I didn't take the 14 updates. I really miss the face to face classes tho. I am sure the seminar guys were talking about this.


Greg Fretwell
Re: Am I the last guy who noticed ... [Re: gfretwell] #219685 10/02/18 06:02 PM
Joined: Oct 2000
Posts: 5,383
S
sparky Offline
Member
Proof old dogs rule Greg

go you!

~S~


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 5
NORCAL 1
Popular Topics(Views)
260,712 Are you busy
195,744 Re: Forum
185,132 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3