what is the minimum dept to the top of a electrical ductbank . low voltage , high voltage
Yoopersup

Nec 2014 Code section

Horizontal Ad
Joined: Mar 2003
Posts: 849
Y
Member
I come up with 2014 NEC page 70-166 Note : Top of Duct or Cable (not concrete) .
Refers you to 300.50 nec page 70-154 . Also see General notes .
What I came up with. Any comments??
Yoopersup

Joined: Jul 2004
Posts: 10,011
Likes: 37
G
Member
That really looks like the general burial requirements and I am not sure you even need enough dirt to grow grass over a concrete duct bank if there is 2" of concrete to the first raceway.
It does seem that when you go too deep you may be making ampacity adjustments but that is starting to get up in that engineering supervision stuff.
I really only dealt with this once, the ducts were over 6 feet down and they had engineers on site. He showed me stamped plans and I said OK.


Greg Fretwell
Joined: May 2005
Posts: 984
Likes: 1
G
Member
I'm installing this exact situation now.
The conduits are being laid in a 6" deep trench (there's a buried structure below it) and concrete will be poured just so people won't have to drive over the round conduits.


Ghost307
Joined: Jul 2004
Posts: 10,011
Likes: 37
G
Member
Traffic is tough on duct banks, That is why they wanted these 6 feet down. Granted this was an interstate tho.


Greg Fretwell
Joined: Apr 2002
Posts: 7,413
Likes: 8
Member
Guys

Looking in the '14 NEC Handbook (Page 272) Figure 310.60

There is a 'Note'
Min burial depth to top of electrical ducts or cables shall be in accordance with 300.50. Max depth to the top of duct banks shall be 30"......etc.

Any specs from the engineer??


John
Joined: Apr 2002
Posts: 7,413
Likes: 8
Member
Just started plan review for an upcoming major project at one of our water utility treatment plants. Two (2) pages of details on the duct banks, some with burial depths of 56" to top of concrete. Details, details, details, which I will 'review' in the next week or so. It is a substantially large project, 350+ page plan set. Funny how the duct bank jumped out as I moved the plan set to my drafting table Saturday afternoon.




John
Horizontal Ad
Joined: May 2005
Posts: 984
Likes: 1
G
Member
I may have used the word "drive" a bit too loosely.
The conduits need to be driven past to get to the last 4 parking spots at the far end of the lot.
There's no thru traffic and anybody going over them should be traveling at a walking pace (unless they're very late for work).


Ghost307

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
363,808 Are you busy
286,713 Re: Forum
265,148 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5