depth of duckbank #219490
08/09/18 05:54 PM
08/09/18 05:54 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 845
Michigan
what is the minimum dept to the top of a electrical ductbank . low voltage , high voltage
Yoopersup

Nec 2014 Code section

2017 / 2014 NEC & Related Books and Study Guides
Re: depth of duckbank [Re: Yoopersup] #219491
08/09/18 06:16 PM
08/09/18 06:16 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 845
Michigan
I come up with 2014 NEC page 70-166 Note : Top of Duct or Cable (not concrete) .
Refers you to 300.50 nec page 70-154 . Also see General notes .
What I came up with. Any comments??
Yoopersup

Re: depth of duckbank [Re: Yoopersup] #219492
08/09/18 09:21 PM
08/09/18 09:21 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,251
Estero,Fl,usa
That really looks like the general burial requirements and I am not sure you even need enough dirt to grow grass over a concrete duct bank if there is 2" of concrete to the first raceway.
It does seem that when you go too deep you may be making ampacity adjustments but that is starting to get up in that engineering supervision stuff.
I really only dealt with this once, the ducts were over 6 feet down and they had engineers on site. He showed me stamped plans and I said OK.


Greg Fretwell
Re: depth of duckbank [Re: Yoopersup] #219493
08/10/18 08:16 AM
08/10/18 08:16 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 947
Chicago Illinois USA
I'm installing this exact situation now.
The conduits are being laid in a 6" deep trench (there's a buried structure below it) and concrete will be poured just so people won't have to drive over the round conduits.


Ghost307
Re: depth of duckbank [Re: Yoopersup] #219494
08/10/18 10:39 AM
08/10/18 10:39 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,251
Estero,Fl,usa
Traffic is tough on duct banks, That is why they wanted these 6 feet down. Granted this was an interstate tho.


Greg Fretwell
Re: depth of duckbank [Re: Yoopersup] #219495
08/10/18 02:47 PM
08/10/18 02:47 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,997
Brick, NJ USA
Guys

Looking in the '14 NEC Handbook (Page 272) Figure 310.60

There is a 'Note'
Min burial depth to top of electrical ducts or cables shall be in accordance with 300.50. Max depth to the top of duct banks shall be 30"......etc.

Any specs from the engineer??


John
Re: depth of duckbank [Re: Yoopersup] #219498
08/12/18 06:06 PM
08/12/18 06:06 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,997
Brick, NJ USA
Just started plan review for an upcoming major project at one of our water utility treatment plants. Two (2) pages of details on the duct banks, some with burial depths of 56" to top of concrete. Details, details, details, which I will 'review' in the next week or so. It is a substantially large project, 350+ page plan set. Funny how the duct bank jumped out as I moved the plan set to my drafting table Saturday afternoon.


John
Re: depth of duckbank [Re: Yoopersup] #219500
08/12/18 09:26 PM
08/12/18 09:26 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 947
Chicago Illinois USA
I may have used the word "drive" a bit too loosely.
The conduits need to be driven past to get to the last 4 parking spots at the far end of the lot.
There's no thru traffic and anybody going over them should be traveling at a walking pace (unless they're very late for work).


Ghost307

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
248,548 Are you busy
186,243 Re: Forum
175,723 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.003s) Memory: 0.9934 MB (Peak: 1.1584 MB) Zlib enabled. Server Time: 2018-08-16 08:13:21 UTC