480 Delta #218983
01/06/18 03:09 AM
01/06/18 03:09 AM
gfretwell  Offline
Joined: Jul 2004
Posts: 9,184
I was talking to a guy from Massachusetts (electronic engineer) and he says 480 delta is common up there for industrial applications. How is that generally grounded? He didn't know but he says he thought it was ungrounded. That did not sound right.
I have seen plenty of 480/277 wye but I have never seen a 480 delta down here.

Greg Fretwell
Work Gear for Electricians and the Trades
Re: 480 Delta [Re: gfretwell] #218985
01/06/18 04:10 PM
01/06/18 04:10 PM
gfretwell  Offline
Joined: Jul 2004
Posts: 9,184
Never mind, we determined that it was corner grounded delta. He just did not realize it.

Greg Fretwell
Re: 480 Delta [Re: gfretwell] #218986
01/06/18 05:57 PM
01/06/18 05:57 PM
ghost307  Offline
Joined: May 2005
Posts: 934
Chicago Illinois USA
We have several mission critical facilities that use an ungrounded delta system.
In the event of a ground fault the system stays energized until it can be corrected.
The only time that the system goes down is when there is a second ground fault before the first one gets cleared.

An ungrounded delta is kinda capacitively coupled to the Earth, so a ground detector device is used.
There are 3 lights wired from phase to a ground rod and all glow continuously at the same brightness.
If one of the phases has a ground fault that light will go out and the other 2 get much brighter.

That tells you which phase the ground fault is on...but finding where it is becomes very challenging.
One of our facilities has had a ground fault on one of the phases for several years...and the maintenance folks are still trying to chase it down.
I think there may be a ground in 2 places on the same phase; which is like trying to find the 2 bad bulbs in an old string of Christmas lights.



2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
kamloops BC Canada
Posts: 1,142
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Trumpy 5
Popular Topics(Views)
244,399 Are you busy
181,512 Re: Forum
171,562 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.9511 MB (Peak: 1.0764 MB) Zlib enabled. Server Time: 2018-03-18 19:25:10 UTC