In Your opinion - What is the biggest , worst, most inconvenient , vague, or best change made in the 2017 NEC ?
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
Luckyshadow
I would like to comment on this....but I have not seen any of the '17 changes as of yet.
NJ is not one to adopt a 'new' NEC quickly. I think when I get back to the office Wed. I'll have one of the clerical staff order the '17.
John
PS: Anyone have any comments??
John
|
|
|
|
|
Joined: Oct 2000
Posts: 4,164 Likes: 6
Member
|
Sorry, I'm not up on the 2017 NEC either.
I think I made a significant change to a prior NEC, but will never get the credit for that.
Bill
Bill
|
|
|
|
|
Joined: Jul 2004
Posts: 10,053 Likes: 40
Member
|
The last time I had a proposal "accepted in principle" was about LEDs in closets. Florida is always a cycle or 2 behind so it will be a while before I get serious about the 17.
Greg Fretwell
|
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
We're on the '17 in Vermont , this new inclusion in 110.14 caused quite the flap >>> 110.14(D) Installation. Where a tightening torque is indicated as a numeric value on equipment or in installation instructions provided by the manufacturer, a calibrated torque tool shall be used to achieve the indicated torque value, unless the equip‐ ment manufacturer has provided installation instructions for an alternative method of achieving the required torque. Apparently someone just had to ask about torque wrench calibration.....and it all went off in the ozone with certifications and qualified testers, etc.... It's Vermont , boring without snow..... ~S~
|
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
This one has many wondering where to purchase what's needed....>> 210.8(B) Other Than Dwelling Units. All single-phase receptacles rated 150 volts to ground or less, 50 amperes or less and three- phase receptacles rated 150 volts to ground or less, 100 amperes or less installed in the following locations shall have ground-fault circuit-interrupter protection for personnel. ~S~
|
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
But by far and large, the one '17 change that left everyone in class with that 'kicked in the pants' look was this>>> 215.2 A 1 Exception No. 2: Where a portion of a feeder is connected at both its supply and load ends to separately installed pressure connections as covered in 110.14(C)(2), it shall be permitted to have an allowable ampacity not less than the sum of the continuous load plus the noncon‐ tinuous load. No portion of a feeder installed under the provisions of this exception shall extend into an enclosure containing either the feeder supply or the feeder load terminations, as covered in 110.14(C)(1). This is hard for me to 'splain , especialy w/o the HB pix . It's essentially saying we can run a feeder @ 90C There's a 1/2 page of if's & buts..... I still don't get it...:( ~S~
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
~s~ It’s been a while, so.....hello & welcome!!
The torque wrench thing will create debate, as you infer about calibrate.
I have to think about you second post a little bit
The third has my head spinning.
John
|
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 2
Member
|
I'd be willing to bet that the torque thing is just to make sure that everyone has one to use instead of trusting the torque standard that we were to at Ford which was "tighten it until it snaps...then back it off a quarter turn". Something tells me that nobody (except perhaps the truly anal AHJ's) will care about having a recent testing certification.
Ghost307
|
|
|
|
|
Joined: Apr 2002
Posts: 7,413 Likes: 10
Member
|
Ghost
FWIW. I know of two AHJs that are going to love the calibration thing..
I do not ‘witness test’, and I am not aware of any other inspectors who want to see/check any torque readings. Basically, it’s on the contractor, or the project design pro/engineer.
John
|
|
|
Posts: 2,724