#218752 09/17/17 09:28 PM
Joined: Feb 2003
Posts: 198
Z
Member
Hi all,
Need to refresh my memories for supporting lb ll lr.
since I don't have a code book around, is it with in 12" or 18'' after the fitting.
Thanks

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2005
Posts: 984
Likes: 1
G
Member
18" for all the conduits entering it.