ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 266 guests, and 9 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#218730 09/04/17 03:43 PM
Joined: Mar 2005
Posts: 240
Member
This is a clarification question about 680.26; "Would it be considered BONDED" If #8 awg bare copper was brought from perimeter surface or pool shell to sub panel of pool equipment and then to motors and heater? In other words, "Do I have to run #8 to the heater or motor first as sub panel wouldn't be required to be bonded to equipotential, however could I? Would adding the sub panel and using its busbar for pool motors and heaters be code compliant?

Thanks,
DeAngelo

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jul 2004
Posts: 10,051
Likes: 40
G
Member
It is not the intent of the equipotential bonding grid to connect to the electrical grounding system. There will be incidental connections via the equipment grounding conductors but the 8ga solid only connects between the required items. (Pool steel, rail/ladder cups, incidental metal within 5', light niche and the electrical equipment)


Greg Fretwell
gfretwell #218732 09/05/17 02:10 PM
Joined: Mar 2005
Posts: 240
Member
Thanks again...

H20

Joined: Jul 2004
Posts: 10,051
Likes: 40
G
Member
It is actually possible to have a pool with no connection at all between the ground electrode and the equipotential grid. It would need a double insulated pump and no other electrical equipment but that is rare.

For most people, the concrete pool is their best grounding electrode although you can't really say it. Those electrons just can't tell the difference.


Greg Fretwell

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5