ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
sec cable code conflict
by jake2018. 11/19/18 01:35 AM
This anti-theist is priceless!!!
by Texas_Ranger. 11/17/18 02:15 PM
High current GFI vs regular GFCI
by Texas_Ranger. 11/17/18 02:07 PM
Single phase and what you call it.
by dsk. 11/12/18 11:10 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 33 guests, and 25 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
600 KW 120/208 3 Phase Y protection #218650
07/20/17 08:56 AM
07/20/17 08:56 AM
Y
Yooperup  Offline OP
Member
Joined: Jul 2017
Posts: 10
mi
Prints say 2500 amp breaker , Name plate 2082 amps .
I say 2000 amp breaker. ???
Yooperup

2017 / 2014 NEC & Related Books and Study Guides
Re: 600 KW 120/208 3 Phase Y protection [Re: Yooperup] #218651
07/20/17 09:44 AM
07/20/17 09:44 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
Yooperup:

As the nameplate is 2082 amps, based on Article 240.6, the OCP can be the next available standard amperage cb or fuse. Keep in mind, the conductors must also be protected for OCP, so you will need 2500 amps or greater of conductor.

Design Professional (EE/PE) prepare plans??


John
Re: 600 KW 120/208 3 Phase Y protection [Re: Yooperup] #218652
07/20/17 12:02 PM
07/20/17 12:02 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,305
Estero,Fl,usa
What type of equipment and is there supplemental overload protection?


Greg Fretwell
Re: 600 KW 120/208 3 Phase Y protection [Re: Yooperup] #218654
07/21/17 08:27 AM
07/21/17 08:27 AM
Y
Yooperup  Offline OP
Member
Joined: Jul 2017
Posts: 10
mi
I talked to the Factory. They Deliver them with 2000 amp breaker or an adjustable trip 2500 amp and dial it down to the generators output which in this case would be 2082. or lower.

Re: 600 KW 120/208 3 Phase Y protection [Re: Yooperup] #218655
07/23/17 08:46 AM
07/23/17 08:46 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Is this a generator? 600kW @ 0.8PF works out to 2082A @ 208V. If you use a 2000A breaker, you won't get the full rated kVA, but that might be OK depending on the power factor and linearity of your load. If you need the full rated 750kVA capacity, you'll need a 2500AF breaker and can use the adjustable trip to get what you need. Be aware there are some other considerations for larger ampacity cabling between the genset and OCP, and often requirements for other protective relays like reverse current and over/under frequency.

This is getting rather large for 208V. If this is new construction, would 480V make more sense? The generator is the same (series vs parallel connection of the windings), but it makes the switchgear, cabling, breakers, and ATS a whole lot smaller and cheaper. Really depends on the nature of your load; there's something to be said for not having a bunch of distribution transformers, too.

Re: 600 KW 120/208 3 Phase Y protection [Re: Yooperup] #218656
07/24/17 11:20 AM
07/24/17 11:20 AM
Y
Yooperup  Offline OP
Member
Joined: Jul 2017
Posts: 10
mi
I agree 480/277 makes more sense but not designed that way.
Adjustable trip breakers on incoming main & generator.
Can dial them down.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,598 Are you busy
188,743 Re: Forum
178,451 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 15 (0.005s) Memory: 0.9771 MB (Peak: 1.1263 MB) Zlib enabled. Server Time: 2018-11-19 12:20:22 UTC