Please note that the opinions herein are my personal opinions, based on guidelines within the NJ UCC, and may be different in other jurisdictions.
Cabling from one piece of equipment to other equipment of the same system, in trays, would require 'listed' trays, bonding, and cabling.
So if it low voltage data cables, it stills needs to be cable tray cable?
Thanks
Data and class 2 gets a big break there. You really just need to keep them neat but your IT guy will have grounding requirements that may exceed art 250.
LarryC Offline OP
http://www.belden.com/docs/upload/Belden-WP-Taking-the-Mystery-Out-of-600V-Ethernet-Applications.pdf
Regulations: NFPA 79 vs. NEC
Virtually all systems employed in manufacturing plants or industrial facilities are subject to the provisions of the NEC, unless they fall under the specific scope of the NFPA 79, the Electrical Standard for Industrial Machinery.
The scope of NFPA 79 is defined as: “The provisions of this standard shall apply to the electrical/electronic equipment, apparatus, or systems of industrial machines operating from a nominal voltage of 600 Volts or less, and commencing at the point of connection of the supply circuit conductors to the electrical equipment of the machine.”
Further, under Section 1.5 of NFPA 79, Specific provisions not made in relation to NEC “On any point for which specific provisions are not made in this standard, the provisions of NFPA 70 shall be observed.”
Additionally, per Section 1.4, Specific provisions other than 79 “…the wiring between component machines of and industrial manufacturing system shall be covered by NFPA 70” with the “Exception: that wiring of component machines of an industrial manufacturing system that is supplied by the manufacturer as an integral part of the system is adequately protected and supported and meets the requirements of this standard.”
Given the above, one would conclude that any field wiring installed and terminated at the manufacturing site – unless done so by the OEM operating under NFPA 79 – would be subject to the provisions and requirements of the NEC, and only field wiring wholly inside the manufacturer supplied electrical or electronic equipment would be subject to NFPA 79
LarryC Offline OP
Information from Belden.
The scope of NFPA 79 is defined as: “The provisions of this standard shall apply to the electrical/electronic equipment, apparatus, or systems of industrial machines operating from a nominal voltage of 600 Volts or less, and commencing at the point of connection of the supply circuit conductors to the electrical equipment of the machine.” Further, under Section 1.5 of NFPA 79, Specific provisions not made in relation to NEC “On any point for which specific provisions are not made in this standard, the provisions of NFPA 70 shall be observed.” Additionally, per Section 1.4, Specific provisions other than 79 “…the wiring between component machines of and industrial manufacturing system shall be covered by NFPA 70” with the “Exception: that wiring of component machines of an industrial manufacturing system that is supplied by the manufacturer as an integral part of the system is adequately protected and supported and meets the requirements of this standard.”
Given the above, one would conclude that any field wiring installed and terminated at the manufacturing site – unless done so by the OEM operating under NFPA 79 – would be subject to the provisions and requirements of the NEC, and only field wiring wholly inside the manufacturer supplied electrical or electronic equipment would be subject to NFPA 79.
Larry:
"So if it low voltage data cables, it stills needs to be cable tray cable?"
800.100 (H) specs a bunch of comm that is OK in tray. IMHO, there is no 'short' answer. With todays cabling being 'a cable of many uses' you should find CT rated/labeled comm with little or no problems. You may consider a 'multi-use' data cable as your "go to".
As Greg said, keep it neat,! Some inspectors will be 'happy' if it's neat and may not look further.
LarryC Offline OP
Thanks for the replies. I dug even further and yes it does get more complicated.
The last two blank posts are where I tried to copy and paste a section of a white paper from Belden cable, about their 600V TC Ethernet cable. It has a 4 paragraph section about where NFPA 79 and 70 apply.
Why it did not post, I do not understand. It looked good in the preview page.
I will bring this up at work tomorrow and we will see what happens.
Larry