Industrail Control Panel bonding per 409.108
#217833
12/08/16 06:17 PM
|
Joined: Jul 2007
Posts: 1,335
OP
Member
|
I may have over think this but I'd rather be safe than sorry. Per 409.108, a bonding main shall be provided when used as service equipment. Am I presuming that this applies only when there's separately derived neutral involved like a. Control transformer? I may be overthinking that with a service switch in the enclosure for the sole purpose of disconnecting the power to the panel and equipment does not constitute as "service equipment" by difinition per NEC. Am I missing something here or am I just missing sleep since I can't wrap my brain around this? Oui vey.....
"Live Awesome!" - Kevin Carosa
|
|
|
Re: Industrail Control Panel bonding per 409.108
[Re: sparkyinak]
#217834
12/09/16 04:42 PM
|
Joined: Apr 2002
Posts: 7,225
Member
|
Sounds like you are wasting gray matter.
IF this is 'service equipment' then you must follow 409.108, if not service equipment.....proceed as usual.
John
|
|
|
Re: Industrail Control Panel bonding per 409.108
[Re: sparkyinak]
#217835
12/09/16 08:49 PM
|
Joined: Jul 2004
Posts: 101
Member
|
"Service Equipment" as defined by being the thing connected to your meter. The rule is there mainly for things like Pumping Plant panels where there is a utility service drop right into a meter, then into the control panel itself. That makes the control panel the Service Equipment, so it needs to follow those rules.
And be labeled / listed as S.U.S.E. by the way.
JRaef
|
|
|
Re: Industrail Control Panel bonding per 409.108
[Re: sparkyinak]
#217836
12/09/16 09:29 PM
|
Joined: Jul 2007
Posts: 1,335
OP
Member
|
That's what I thought but I over thunked it. Thanx
"Live Awesome!" - Kevin Carosa
|
|
|
|
|