Hey guys. I just went to troubleshoot a large grow room. Breakers are tripping for the 36 - 1000w HPS lighting. The building is 208v, the lighting is 240v.

I unplugged all the ballasts and fired up the breakers and contactors. Everything held and no tripping breaker. I tested voltage at contactors and receptacles, everything is 'OK'. I told the guy looks like hes got some bad ballasts.

I started plugging in 1 ballast at a time to try and find the bad ballast. Well come to find out every ballast is bad. Most are just not working, a few others pop'd, sparked and smoked. After the 2nd pop, spark and smoke I stopped.

Scratched my head for a few minutes.

Went back to test the contactors. I killed power to the coil and tested the contactors in the normally off position. There was voltage on the load side while the contactor was off!

I'm thinking the contactor failed and when it shut off it didn't shut off fully and must of sent 208v down a leg and fried the ballasts. Quite odd it happened to all 4 contactors.

Hes running these same contactors and same load in another room and its been fine for 6 months.

The stats on the contactor are: FL=40a, RES=50a. The load was 9000w of HPS lighting powered by an electronic ballast.

I told him his contactors are overloaded and basically welded together, creating 208v down 1 leg and destroying his 36 ballasts. $10,000 in damages. He had a hard time believing it, saying the contactors are rated for 50a and they shouldn't do that. I told him they should be rated atleast 20% higher... I was talking outta my ass at this point cause I really don't know. smile

Can you guys give your opinion on this and tell me the proper sizing for the contactors. Or maybe he needs a different type of contactor, idk. My contactor experience is little.

Last edited by Trick440; 06/10/16 05:52 PM.

Shake n Bake
Horizontal Ad
Joined: Apr 2002
Posts: 7,403
Likes: 7
Member
Trick:
It was a tough day today for me, but....

You said bldg. is '208' and lighting is '240'; is there any buck-boost transformers in the circuit?? Or are the ballasts on the 208 taps??

Get the info off of a ballast regarding 'operating' and 'start-up' amps, then check your ratings.

Did you clamp the loads on the contactors in the 'other room'??

How do you figure "208v down 1 leg"??

Last edited by HotLine1; 06/10/16 08:55 PM.

John
Joined: Jan 2005
Posts: 5,474
Likes: 3
Cat Servant
Member
When you say 'grow room,' I start thinking of all manner of hackwork, using fixtures salvaged from dumpsters, to grow forbidden substances.

Please note that contactors carry a specific rating for HID lighting. An ordinary 'definite purpose contactor' is not rated for HID lighting.

Likewise, fixtures need to be supplied with power within 10% of their nameplate voltage. A "240" rated fixture is not suitable for use with 208v. Not every ballast is a multi-tap, or "automatic," especially with the old, obsolete HPS lights.


Joined: Aug 2005
Posts: 251
T
Member
I'm sorry guys I'm more residential. I put my tester on it and it was 220v or somewhere in the 200s and I just jumped to the conclusion its 208v. Is there a 3ph high leg that is 220v?

I didn't test anything in the other room. The ballasts are from what I'm told 120 or 240 automatic. Same as in the other room. http://www.galaxyballasts.com/shop/...asts/galaxy-grow-amp-electronic-ballasts

Reno, they have a bit more than salvaged fixtures from a dumpster. From the new 1200a service, RTU and all the other gadgets I'd guess they have $200k+ into it.


Shake n Bake
Joined: Aug 2005
Posts: 251
T
Member
To clarify when I tested any 2 legs gave me 240v. When I tested the legs to ground, 2 read 120v and the high leg read 210v+ (I'm not sure the actual number for this high leg I seen it around 208v it stuck in my head its a 208)

Last edited by Trick440; 06/10/16 11:35 PM.

Shake n Bake
Joined: Sep 2002
Posts: 946
Likes: 2
N
Member
Originally Posted by Trick440
To clarify when I tested any 2 legs gave me 240v. When I tested the legs to ground, 2 read 120v and the high leg read 210v+ (I'm not sure the actual number for this high leg I seen it around 208v it stuck in my head its a 208)



240V 3Ø has 2-phases 120V L-N, & what is supposed to be the B phase 208V L-N, any phase to phase should be 240V, 208Y/120V has
L-N of 120V, L-L is 208V just a note, a "slash rated" 120/240V breaker cannot be used between the high leg and any other phase, expensive 240V rated breakers have to be used.

Joined: Aug 2005
Posts: 251
T
Member
Ok thank you for the clarification. It seems this is a Delta 120/240, 3ph has always confused me.

I'll have to check the breakers to see if its 240v rated breakers.

Do we think the improper contactors and possible wrong breakers could have fried the ballasts? Anything else I should investigate for this repair?


Shake n Bake
Horizontal Ad
Joined: Sep 2002
Posts: 946
Likes: 2
N
Member
Originally Posted by Trick440
Ok thank you for the clarification. It seems this is a Delta 120/240, 3ph has always confused me.

I'll have to check the breakers to see if its 240v rated breakers.

Do we think the improper contactors and possible wrong breakers could have fried the ballasts? Anything else I should investigate for this repair?



To my knowledge 240V rated breakers are only required where the high leg and another phase are being used for a 240V circuit.

Joined: Apr 2002
Posts: 7,403
Likes: 7
Member
Interesting link to the ballasts.....

$ 279.99 gets you a 240 volt, adjustable wattage, cord & plug connected ballast. The available info at the site, includes weight, dimensions, UPC #, but there is NOT one electrical piece of info. This would be the first 'cord & plug' connected ballast I have seen.



John
Joined: Jul 2004
Posts: 9,998
Likes: 35
G
Member
Is that a ballast for a double ended lamp?
I wonder if that is simply referring to the 410.30(G)(1) disconnect? (using a plug)



Greg Fretwell
Page 1 of 3 1 2 3

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
331,573 Are you busy
256,790 Re: Forum
238,636 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5