ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 1,002 guests, and 9 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Jul 2007
Posts: 264
W
Member
Greg, off the cuff I am going to say neutral leakage, because the breaker would not reset with the light hooked up and the switch turned off. I did not measure voltage from ballast to case after isolating them.
John, I did try with the ground unhooked but figured it would not help as the dock is all aluminum and of course bonded at every possible location, and the lights are mounted on aluminum boxes. I will update when/if Lithonia replies and what the solution is.


Jimmy

Life is tough, Life is tougher when you are stupid
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Nov 2005
Posts: 826
Likes: 1
J
Member
I'll bet that Greg is right and that they got sloppy on their RF bypassing. If you hook it up non-gfci, and measure the ground current with your Fluke on AC mA, you will probably observe enough current for a legit gfci trip.
Joe

Page 2 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5