110.26(E) #216947
03/18/16 02:51 PM
03/18/16 02:51 PM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
Since most large switchboards placed along a wall tend to be positioned at least a few inches off/away from said wall, does the code allow foreign equipment to be mounted within this gap and under 6' above the electrical equipment? Tecnically, nothing placed within this gap would be within the "footprint" of the gear. Obviously, at some point, the gap does become large enough for other trades to use. Is it one inch, three inches, one foot? Can the AHJ say that even 18" isn't enough?

2017 / 2014 NEC & Related Books and Study Guides
Re: 110.26(E) [Re: triple] #216948
03/18/16 04:12 PM
03/18/16 04:12 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 958
Chicago Illinois USA
Check with your AHJ.
I know that although Chicago says no (because they prohibit foreign items within the footprint and the associated working space); it is allowed in other cities.


Ghost307
Re: 110.26(E) [Re: triple] #216954
03/19/16 01:37 AM
03/19/16 01:37 AM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
The working space is only in front of the type of equipment I am referring to. For equipment requiring working space behind it, the unit would not be allowed to be placed up against a wall. Sorry, I don't think I described the situation very clearly.

Re: 110.26(E) [Re: triple] #216956
03/19/16 12:10 PM
03/19/16 12:10 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 958
Chicago Illinois USA
I really think the AHJ needs to weigh in on this.
A drain line behind the equipment will cause few problems, a water line could sweat or break, a gas line is a hazard next to electrical equipment.
You also have to consider how you would repair/replace something that is rendered inaccessible after installation.
The 2 of you need to go over the specifics of this installation...I doubt that there is a universal answer to this.


Ghost307
Re: 110.26(E) [Re: triple] #216957
03/19/16 01:53 PM
03/19/16 01:53 PM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
1) The area I am referring to is above the equipment, within six feet vertically of its top, but behind the footprint. If the equipment were 6' from the wall instead of 4" then there would definately be no problem with anything foreign being installed there.
2) Nothing is rendered inaccessible. Again, I must not have described the scenario well. Nothing has been placed directly behind the switchgear. It it above but behind the footprint.

Re: 110.26(E) [Re: triple] #216970
03/21/16 09:34 AM
03/21/16 09:34 AM
A
ampherder  Offline
Member
Joined: Sep 2011
Posts: 20
VA
The way 110.26(E) is worded, there would be nothing prohibiting what you describe. The AHJ can always choose to rule differently.

Re: 110.26(E) [Re: triple] #216976
03/22/16 09:57 AM
03/22/16 09:57 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,036
Brick, NJ USA
IMHO, it would depend on the proposed 'foreign' item is. Any 'item' that may 'leak' or cause any type of damage to the gear would be a "No", unless protection of the gear could be maintained.

The best solution to your inquiry would be a discussion with the local AHJ.


John
Re: 110.26(E) [Re: triple] #216977
03/22/16 10:57 AM
03/22/16 10:57 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 958
Chicago Illinois USA
Agreed.
I had a major switchgear installation where the Contractor took a short cut and routed the incoming natural gas line over the gear.
His response to the AHJ's objection was to put a drip pan underneath the gas pipe.

As the old adage goes...you can't fix stupid.


Ghost307

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,525 Are you busy
188,086 Re: Forum
177,719 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.006s) Memory: 0.9931 MB (Peak: 1.1573 MB) Zlib enabled. Server Time: 2018-10-21 08:36:57 UTC