Double check the boss's work #216035 09/12/15 10:20 AM
Joined: Feb 2013
Posts: 264
Potseal Offline OP
Member
My boss planned the job and then I was asked to execute it. Place a UPS in front of the controls for a small gas fired boiler. Seemed simple enough. Once everything was in place I did a test and watched the UPS shutdown on overload. Then I started doing what I should have done in the first place - check the details of the installation. The UPS output was insufficient. The inrush for the fan motor was 31A and the UPS output is 12.5A. The default overload setting is >102% with a max setting of >150% (for 100ms). Right on the boiler controls itself it states that a minimum circuit ampacity of 13.25A is required. Red flags all over the place if I had only taken a few minutes to double check the details. My boss is an experienced electrician who seldom makes these types of mistakes. Looks like I'll have some bad news for him on Monday morning. Gotta love Mondays.


A malfunction at the junction
--------------------------------------
Dwayne
Work Gear for Electricians and the Trades
Re: Double check the boss's work [Re: Potseal] #216038 09/14/15 01:31 PM
Joined: Apr 2002
Posts: 7,123
HotLine1 Offline
Member
Another example of 'we are all human'.

Time for a larger capacity UPS.


John
Re: Double check the boss's work [Re: HotLine1] #216039 09/15/15 08:20 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
How about the factory's work? Good one was, I wired in a large electric fan. Sounded like a C-130 taking off but everything checked out. A few weeks later, I got called backed because the motor flamed out. It was properly protected but the end users were resetting the tripped over loads thinking it was a timer controller.

Get a new motor, sounds like a C130 taking off and I put my amp clamp on it. This time it's over loading. Get my bosses amp clamp and it reads the same. When I originally installed the fan, my amp clamp read good. I put the old battery back in my meter which was weak and was getting bad readings. Needless to say, I deep sixed that meter

Back to the new motor. I tried everything, triple checked my wiring, sizing of wires, adjusted the motor to try to minimize the air captured by the fan. No dice. Told my boss that the only thing I could figure the motor for was the wrong size for the fan. He wigged out yelling, "you telling me the factory is churning out hundreds of theses with the wrong motor!?! Bull puckey!"

A few days later, my boss calls me in and says, "remember that fan motor? They put the wrong motor in it. They are sending the proper one.".....


"Live Awesome!" - Kevin Carosa
Re: Double check the boss's work [Re: Potseal] #216047 09/16/15 03:56 PM
Joined: Oct 2006
Posts: 745
E
EV607797 Offline
Member
I've run into this with furnace blowers a lot. One nameless manufacturer produced hundreds of them in my area as heat pump system sections that were equipped with 1/2 HP motors instead of the proper 1/3 HP ones. We chased our tails for months, eventually changing the taps to the lowest speed so that they would at least run continuously.

Another contractor in the area finally figured out the issue and contacted the manufacturer's local rep. Fortunately, they provided replacement blower assemblies free of charge and paid us about $100.00 each to replace them.

Yes, the factory does make mistakes. Sometimes, they can be very costly ones.


---Ed---

"But the guy at Home Depot said it would work."

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 2
andey 2
Popular Topics(Views)
261,489 Are you busy
196,670 Re: Forum
185,913 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3