ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Video door bell causing chime activation of coil
by gfretwell. 12/16/18 09:01 PM
Pull out fuse panel?
by wa2ise. 12/14/18 05:09 PM
Conduit fill Calculations
by gfretwell. 12/08/18 08:39 PM
Swimming Pool question
by HotLine1. 12/05/18 12:37 PM
Tingle off the water spigot
by rmiell. 11/30/18 01:03 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 4 guests, and 24 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Unfused surge protection #215603
06/08/15 12:55 AM
06/08/15 12:55 AM
T
twh  Offline OP
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Is it normal to install surge protection without a breaker? The surge protection in question has fuses and is on an 800 amp cdp. How would you change fuses without shutting down everything on the cdp, like the servers, office computers on three floors, the lights and the elevator?

[Linked Image]

Work Gear for Electricians and the Trades
Re: Unfused surge protection [Re: twh] #215604
06/08/15 01:58 AM
06/08/15 01:58 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,324
Estero,Fl,usa
I agree this may be a poor design but if there are fuses in the SP, it is legal. I suppose with the right PPE and tools you could change the fuses hot but the only reason they would fail is a fault in most cases (shorted MOV) and the new fuse is going to "flashbulb" most of the time.
I would put it on a breaker.


Greg Fretwell
Re: Unfused surge protection [Re: twh] #215612
06/09/15 06:52 PM
06/09/15 06:52 PM
W
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 788
Oradell NJ USA
If this box claims to clamp transients of a few nanoseconds, the coil usually in circuit breakers may interfere with that. The coils would look like a high impedance to transient spikes that short. However, most power supplies in servers and computers contain filtering coils of much higher inductance, so such short transients shouldn't be much of an issue.

For longer transients, the circuit breaker shouldn't be an issue.

Re: Unfused surge protection [Re: twh] #215613
06/10/15 08:38 AM
06/10/15 08:38 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
As this is in Canada, IF the install is compliant with the CEC, it also conforms to the mfg. install guidelines.

"2.1.4 Wiring
Turn OFF the power to the electrical distribution
equipment where the CPS Filter is to be installed.
Install a branch circuit breaker to feed the CPS filter
device for ease of installation. The unit contains UL
and CSA approved fusing to protect against short
circuit fault conditions within the device.
Over current protection is not specifically required,
although most customers choose to install a circuit
breaker as a disconnect device on panelboards or
switchgear assemblies. (See Table 2 for suggested
circuit breaker size). Follow NEC, CEC and applicable
local codes when connecting the CPS directly to the
Bus Bar."

IMHO, a branch circuit CB as suggested within the guidelines would be the way to go, and how all I have seen are installed.


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,249 Are you busy
189,209 Re: Forum
178,891 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.004s) Memory: 0.9618 MB (Peak: 1.0962 MB) Zlib enabled. Server Time: 2018-12-17 07:25:17 UTC