Laundry Circuits #215362 04/15/15 11:34 PM
Joined: Mar 2004
Posts: 750
B
BigB Offline OP
Member
If I provide an another circuit in the laundry in addition to the required 210.11(C)(2)branch circuit can this additional circuit have other outlets, like say an outdoor receptacle or two?

2017 / 2014 NEC & Related Books and Study Guides
Re: Laundry Circuits [Re: BigB] #215363 04/16/15 01:45 AM
Joined: Jul 2004
Posts: 9,435
G
gfretwell Offline
Member
Yes, They only require one dedicated circuit 20a for the "laundry" but there can be other general lighting circuits in the room.


Greg Fretwell
Re: Laundry Circuits [Re: BigB] #215364 04/16/15 10:27 AM
Joined: Mar 2004
Posts: 750
B
BigB Offline OP
Member
Thanks Greg. Specifically this extra circuit will be for two counter top receptacles in the laundry and one outdoor receptacle, all 20 amp GFCI protected. What got me thinking about it is the argument about the kitchen SABC circuits, no matter how many you provide after the required two they still cannot have other outlets except dining, nook, pantry etc. as I understand it, and as my jurisdiction enforces it.

Last edited by BigB; 04/16/15 10:28 AM.
Re: Laundry Circuits [Re: BigB] #215365 04/16/15 12:17 PM
Joined: Jul 2004
Posts: 9,435
G
gfretwell Offline
Member
I think difference is that 210.11(C)(2) says "this circuit" when describing the laundry circuit. 210.52(B)(2) says "The two or more small-appliance branch circuits" implying all of them.
I suppose you need to ask your AHJ for the answer that applies in his patch.

At a certain point this dedicated circuit thing does go just a little nuts.


Greg Fretwell
Re: Laundry Circuits [Re: BigB] #215366 04/16/15 02:29 PM
Joined: Apr 2002
Posts: 7,133
HotLine1 Offline
Member
I agree with Greg.
Talk to your local AHJ for his take


John

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 233
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
dsk 7
Trumpy 6
Popular Topics(Views)
262,506 Are you busy
197,645 Re: Forum
186,645 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3