ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Changing a Bulb
by gfretwell. 07/14/18 03:12 PM
Tray cable?
by gfretwell. 07/11/18 10:18 PM
Eaton Heavy Duty 30A and 60A Safety Switches
by Admin. 07/11/18 09:49 PM
ORTOVOX Recalls Avalanche Transceivers
by Admin. 07/11/18 09:44 PM
Tingle off the water spigot
by gfretwell. 07/08/18 12:58 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 11 guests, and 18 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Portable UPS on isolated ground circuits #215212
03/23/15 04:48 PM
03/23/15 04:48 PM
S
sparkyinak  Offline OP
Member
Joined: Jul 2007
Posts: 1,334
Alaska
Hi,

Maybe one of you can save me some homework. Any reason not to plug a portable UPS is isolated ground circuits?


"Live Awesome!" - Kevin Carosa
Work Gear for Electricians and the Trades
Re: Portable UPS on isolated ground circuits [Re: sparkyinak] #215213
03/23/15 06:11 PM
03/23/15 06:11 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
I can't think of anything.
I do think IG is largely snake oil tho.
IBM stopped recommending them about 40 years ago. There was no demonstrated benefit.


Greg Fretwell
Re: Portable UPS on isolated ground circuits [Re: gfretwell] #215214
03/23/15 08:47 PM
03/23/15 08:47 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 946
Regina, Sask.
Originally Posted by gfretwell
I can't think of anything.
I do think IG is largely snake oil tho.
IBM stopped recommending them about 40 years ago. There was no demonstrated benefit.
I don't know about that. I did quite well off them.

Re: Portable UPS on isolated ground circuits [Re: sparkyinak] #215215
03/23/15 10:37 PM
03/23/15 10:37 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
IG came to be quite the 'cause' when computers entered filthly electrical systems.

To go down the list:

Crossed over polarities -- far, far, more common than they should be -- so many out there tying their best to give us more repair work...

Over loaded circuits -- until digital logic came along sagging voltages passed largely without remark...

&&&&&

I've never encountered an IG installation in commercial service that was not companion to an isolated power system: an SDS. ( Secondarily Derived Service )

They went together like bread and butter.

It was a LOT cheaper to just drop these in rather than re-work and correct a fundamentally screwed up building -- some of which were bona-fide antiques.

Now that decades have gone by -- and ABOVE ALL -- with the rise of laptops in general office use (which have intrinsic isolated power and secondarily derived services -- every last one) the passion for IG and isolated power has evaporated.

It won't be coming back any time soon.



Tesla
Re: Portable UPS on isolated ground circuits [Re: sparkyinak] #215216
03/24/15 03:56 AM
03/24/15 03:56 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
The dirty little secret was IBM figured out they had found the enemy and it was us.
Virtually all of the noise in office electrical systems was coming from the switcher power supplies in our equipment.
When we put in the line filters we should have been using from the git go, it stopped being an issue.


Greg Fretwell
Re: Portable UPS on isolated ground circuits [Re: sparkyinak] #215219
03/24/15 02:24 PM
03/24/15 02:24 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,985
Brick, NJ USA
IG circuits, panels, and receptacles generated a lot of $$$ back in the day.

The search for 'clean power' for the electronics gurus went to motor/generator sets, and active UPS units. That was not your 'standard' offices, but research & prototype EEs in the 'chip making' fields.



John
Re: Portable UPS on isolated ground circuits [Re: sparkyinak] #215220
03/25/15 12:54 AM
03/25/15 12:54 AM
S
sparkyinak  Offline OP
Member
Joined: Jul 2007
Posts: 1,334
Alaska
My neck of the woods is largely behind the times electrically. I have offices wired in Romex of a marginal utility not connect to a grid, no IG, No surge protection, ground rod and connection to water pipe ground, frequent brown, blackouts, spikes from eagles flying into the lines, diesel generator back up and no problem with electronics. The more protected systems, like IG, ground rings, system wide surge protection, overrides neutrals, and the like seem have more problems. Lol!


"Live Awesome!" - Kevin Carosa

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,142 Are you busy
185,601 Re: Forum
174,942 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.003s) Memory: 0.9870 MB (Peak: 1.1447 MB) Zlib enabled. Server Time: 2018-07-20 18:14:51 UTC