Receptacle ground prong - Up, down, left, right... #215016
02/22/15 03:32 AM
02/22/15 03:32 AM
S
sparkyinak  Offline OP
Member
Joined: Jul 2007
Posts: 1,334
Alaska
Which way and why?.... and go!

Sorry folks, I had to do it....


"Live Awesome!" - Kevin Carosa
Work Gear for Electricians and the Trades
Re: Receptacle ground prong - Up, down, left, right... [Re: sparkyinak] #215018
02/22/15 12:23 PM
02/22/15 12:23 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,266
Fullerton, CA USA
laugh

There was an article in EC&M about 11 years ago titled "Mr. Addiss' Neighborhood". (I can't find it now, it probably has been removed)

It dealt with the various online communities.

Bill said he wanted to create a Forum where the question of up or down wasn't in every other post.

Member Big John wrote: 4/23/04

"Neat! With an article like that, I bet there'll be a jump in membership soon enough.

But that article reminded me of something: I have this grounded receptacle here and..." grin


That was the last mention, until now.

Over 10 years is a pretty good record of success!

yay



Re: Receptacle ground prong - Up, down, left, right... [Re: sparkyinak] #215019
02/22/15 02:12 PM
02/22/15 02:12 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,967
Brick, NJ USA
Recently, I have seen up and down on the same office renovation.

Seriously, one EC does 'up' for any switched outlets; that's a nice touch when doing inspections.

Other then that.....let the debate go....


John
Re: Receptacle ground prong - Up, down, left, right... [Re: sparkyinak] #215020
02/22/15 02:38 PM
02/22/15 02:38 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
John, that's my style, too -- for residential.

It, the switched receptacle, just doesn't exist in my commercial work. (Lumières)

It saves a LOT of grief -- as you'll get phone calls about a dead socket -- which can be solved by a simple query: "Hey, is the ground -- the third pin -- facing UP?"

&&&&





Tesla
Re: Receptacle ground prong - Up, down, left, right... [Re: sparkyinak] #215021
02/22/15 02:40 PM
02/22/15 02:40 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 940
Regina, Sask.
I like my cords with angle ends to hang down. My washer and dryer cords are both ground down. Welder plugs that I've installed are ground up.

If my washer and dryer cords were ground up, I might change the plugs. Or, I might just watch TV, instead.

As to changing the orientation for switched plugs, unless you put a note on the switch, the customer won't know, and if you are going to label something, just label the plug.

It's like arguing whether plugs should be white, brown, black, ivory, light almond... It's the customer's decision to make. If they don't care, why would I?

Re: Receptacle ground prong - Up, down, left, right... [Re: sparkyinak] #215022
02/22/15 02:58 PM
02/22/15 02:58 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
In the electrical world, worrying about plug orientation makes about as much sense as the Captain of the Titanic worrying about the placement of deck chairs.

It's far more important that it BE there ... AND be connected to a good path back to the service.

Personally, I like the traditional "Mister Smiley" placement. I also like the upside-down placement for switched receptacles.

Most important, though, I like to place the receptacle so as to cause the least strain on the plug. I really don't like to see an 'angle' plug with a sharp bend in the cord. The situation most often comes up with ranges, dryers, and air conditioners - though vending machines are also an issue.

With those situations, we're not really talking about receptacle orientation; we're really just trying to make up for poorly placing the receptacle in the first place.

The person who adamantly argues for a particular orientation is often the same person who places receptacles to "code minimum," customer comfort be damned. Hence, all those contorted plugs behind furniture.

Job specifications will often call for a certain orientation. While I have no objection to the specification as such, I do shake my head at the implied micro-management. It's almost a warning that some unqualified engineer type has assumed instant expertise, based on nothing more than the arrogance of a job title.

Re: Receptacle ground prong - Up, down, left, right... [Re: sparkyinak] #215023
02/22/15 03:15 PM
02/22/15 03:15 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,266
Fullerton, CA USA
We built a Kindercare Day Care once where their company policy was that the grounds be up.(and mounted +54"AFF)

Their rationale was that if installed down the receptacles would look like smiley faces smile to the children.
I'll bet they have all been retrofitted to tamper proof recps by now

laugh ...and that's the only sound argument I've ever heard.

Re: Receptacle ground prong - Up, down, left, right... [Re: sparkyinak] #215024
02/22/15 04:18 PM
02/22/15 04:18 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,225
Estero,Fl,usa
I notice the plug manufacturers seem to favor pin down but I have some that seem to favor pin up although they may be assuming the equipment is higher than the receptacle.


Greg Fretwell
Re: Receptacle ground prong - Up, down, left, right... [Re: sparkyinak] #215032
02/24/15 12:47 AM
02/24/15 12:47 AM
Potseal  Offline
Member
Joined: Feb 2013
Posts: 264
Saskatchewan
I once read through a similar discussion somewhere on the web. One individual was in favour of the pin being down. He tried to rationalize his preference by stating that if the receptacle is in that orientation and the cord end starts to pull away from the wall in a downward direction that the ground pin would be the last to lose contact.

I personally install the receptacle in whatever direction makes most sense. If I know that a certain piece of equipment will be sitting in front on a permanent basis and the manufactured cord end has a 90 degree then I might orientate the receptacle to best suit the way in which the cord can be tucked in back without getting in the way or putting stress on it.


A malfunction at the junction
--------------------------------------
Dwayne
Re: Receptacle ground prong - Up, down, left, right... [Re: sparkyinak] #215038
02/24/15 05:58 AM
02/24/15 05:58 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
The counter argument goes, that the live pins are protected during partial insertion with the ground pin UP... which is the longest pin... so that it makes first and breaks last....

So that in a classroom it's best to have ground pins UP so that any falling object (hair pin?) is deflected by a grounding conductor. By the time the grounding pin is out of the socket, the others, hot and return, are also disconnected.

Partially engaged power cords are ten-a-penny in America's classrooms, for someone is sure to step on the cord as it drapes out of the wall socket.

As for utilization equipment in such settings: I'd favor devices with ninety-degree cord caps.

Due to the ADA statutes, I've been raising my normal receptacle heights UP. What used to be, say, a foot -- is now uniformly at least 18" (on center) AFF.

The advent of the LaserJamb has changed my procedures. I now set the LaserJamb, first, and then use it's horizontal beacon to set all boxes to a perfectly level height.

This is especially slick in old work renovations -- where plumb, square and true are mere suggestions.

http://www.fastcap.com/estore/pc/LJ3Pro-Laserjamb-3p18.htm

https://www.youtube.com/watch?v=ywKWxs_arnU

^^^ The original video demonstration


Tesla
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,236
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
twh 7
Popular Topics(Views)
246,952 Are you busy
184,349 Re: Forum
173,556 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 16 (0.004s) Memory: 1.0312 MB (Peak: 1.2151 MB) Zlib enabled. Server Time: 2018-05-28 08:12:38 UTC