Minimum height for disconnect on mobile home #214818
01/28/15 07:33 PM
01/28/15 07:33 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Somewhere is the previous codes I remember the minimum height of a disconnect on a mobile home was 2 ft. I have a potential job that the meter and panel is burnt up, and needs replacing. The height now is only 18 inches, and it will have to be dropped about 2 or 3 inches so that the wires will reach the new "feed thru" panel. I can't seem to find it in the 2011 code book I'm looking in. Can anyone help me find this. I talked with the local inspector and he didn't seem to know and said I might have to run new wires to the inside panel to get the panel high enough. Thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Minimum height for disconnect on mobile home [Re: sparkync] #214820
01/28/15 09:04 PM
01/28/15 09:04 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
This is the first I have heard of a 'minimum' level. If there were one, I expect it would be found in the standards of the local PoCo.

PoCo standards are not binding when the park does its' own billing.

"Standard" Service pedestals seem to place the meter at about the 4-ft. level. Such pedestals have, as part of their base, an accessible trough that extends into the ground. I would expect that you can splice the wires in that trough, to reach where you must.

How to splice? My first choice would be crimps, wrapped in tape and covered with Scotchkote. NSI's Polaris connectors would be my next choice, similarly sealed with Scotchkote.

Re: Minimum height for disconnect on mobile home [Re: sparkync] #214823
01/28/15 09:54 PM
01/28/15 09:54 PM
G
ghost307  Online Content
Member
Joined: May 2005
Posts: 951
Chicago Illinois USA
It's in 550.32.


Ghost307
Re: Minimum height for disconnect on mobile home [Re: sparkync] #214824
01/29/15 12:50 AM
01/29/15 12:50 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
Ghost is right on

Quote
(F) Mounting Height. Outdoor mobile home disconnecting means shall be installed so the bottom of the enclosure containing the disconnecting means is not less than 600 mm (2 ft) above finished grade or working platform. The disconnecting means shall be installed so that the center of the grip of the operating handle, when in the highest position, is not more than 2.0 m (6 ft 7 in.) above the finished grade or working platform.


Greg Fretwell
Re: Minimum height for disconnect on mobile home [Re: sparkync] #214826
01/29/15 01:26 AM
01/29/15 01:26 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Thanks a lot. I knew it used to be in there. I just couldn't find it.

Re: Minimum height for disconnect on mobile home [Re: sparkync] #214828
01/29/15 01:57 AM
01/29/15 01:57 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
If I put a pvc junction box under the panel to make splices, and have 2" pvc coming in one side from the bottom and 2"pvc going out the other side up to the panel, will the size of the junction box have to be at least 12" since 314.28 (2) says that it must be 6 times the largest raceway entering the box? My other question would be how deep would it have to be? 12x12x12? or could it be 12x12x8 ?? sort of confused on the depth.

Re: Minimum height for disconnect on mobile home [Re: sparkync] #214830
01/29/15 05:19 AM
01/29/15 05:19 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
I don't think the depth is addressed directly but you still need enough volume for the fill. This is mainly just addressing the bending space laterally


Greg Fretwell
Re: Minimum height for disconnect on mobile home [Re: sparkync] #214832
01/29/15 11:01 AM
01/29/15 11:01 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Thanks Greg. I couldn't see that it was either.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 9
Popular Topics(Views)
249,437 Are you busy
187,353 Re: Forum
176,694 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.004s) Memory: 0.9952 MB (Peak: 1.1560 MB) Zlib enabled. Server Time: 2018-09-24 17:29:58 UTC