Conduit fitting question #214759 01/22/15 02:40 PM
Joined: Apr 2013
Posts: 22
S
sedesigner1 Offline OP
Member
We are installing a new oil filled transformer and will be penetrating the oil pit liner. The drawings indicate the conduit immediately turning up to a field termination cabinet. The conduit is 4" sch 40 PVC, the cable will be 3-1/C 350kcmil. The engineer says the conduit needs to penetrate the liner at a right angle and to use a 90 degree LB fitting to turn up as we don't have room for a sweep. As this will later be filled with stone, is it acceptable to use an LB fitting that will be below grade? I've never done this before, but am drawing a blank if it's permissible. Thanks for any input. Greg

Work Gear for Electricians and the Trades
Re: Conduit fitting question [Re: sedesigner1] #214760 01/22/15 03:57 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Not Permitted. You must retain access to that LB when installation is complete, just as if it were a junction box.

Invariably, someone at this point will say "but we can remove the stones later." They might even find code language that would allow, say, minor amounts of leaf mulch to conceal outdoor lighting fittings. Nice try; we might as well just eliminate any restrictions on accessibility if we're going to stretch that loophole that far.

You'd be better using another code provision that might let you re-examine 'conduit fill,' and make a sweep using a conduit barely large enough for the cable to enter. Or, for that matter, use a cable that's rated for direct burial.

Re: Conduit fitting question [Re: renosteinke] #214761 01/22/15 04:19 PM
Joined: Apr 2013
Posts: 22
S
sedesigner1 Offline OP
Member
Renosteinke, thanks for the quick response. That's what I thought, treat the LB like a junction box, you need to retain access. I told the engineer, and he agreed to look for a different solution. I appreciate the quick input. Best regards, Greg

Re: Conduit fitting question [Re: sedesigner1] #214762 01/22/15 04:39 PM
Joined: Apr 2002
Posts: 7,178
HotLine1 Offline
Member
You may consider a 'Quazite' box adjacent to the pit; punch thru the sidewall of the box into the pit and exit at 90 degrees either right or left side & up.

The LB would be a red tag.





John
Re: Conduit fitting question [Re: sedesigner1] #214764 01/22/15 07:36 PM
Joined: Apr 2013
Posts: 22
S
sedesigner1 Offline OP
Member
John, I'm having a hard time picturing your solution. I guess I'm missing something in the translation. Could you further explain? We've put this on hold so I have some time to complete.
Thanks, Greg

Re: Conduit fitting question [Re: sedesigner1] #214765 01/22/15 09:43 PM
Joined: Apr 2002
Posts: 7,178
HotLine1 Offline
Member
OK, I'll try...
A 4" nipple out of the side of the pit, and into the side of a 'quazite' box of suitable depth and bending spaces for your conductors.

Basically think like a j-box adjacent to the tranny pit. Then exit the 'box' from either side to your cabinet.



John
Re: Conduit fitting question [Re: sedesigner1] #214766 01/22/15 10:09 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Another bit of code trivia:

The accessibility requirement for the LB would also apply to a 90 degree fitting for "Flex" or "Sealtite." The requirement does not apply, however, to MC. "MC" is best described as flex that is sold with the wires already in it.

Whether there is a rated MC and fitting for your application is another question.

Re: Conduit fitting question [Re: sedesigner1] #214767 01/22/15 10:45 PM
Joined: Apr 2002
Posts: 7,178
HotLine1 Offline
Member
I've seen MC that was suitable for under slab and concrete encasement, it had/has a PVC exterior jacket, and special connectors.

There could be an issue with bend radius.

This may be an idea, but...availability?? minimum length??
Is it 'made to order', or warehouse stock?

I only saw it on one job, at least 5-8 years back.



John
Re: Conduit fitting question [Re: sedesigner1] #214772 01/23/15 01:20 AM
Joined: Dec 2000
Posts: 4,283
electure Online Sleepy
Member
Southwire's current price sheet lists it's PVC coated MC cable at $79.80 a foot for 3-350kcm with a ground



Re: Conduit fitting question [Re: sedesigner1] #214776 01/23/15 10:57 AM
Joined: Apr 2002
Posts: 7,178
HotLine1 Offline
Member
Thanks Electure, this may help the OP.

100' minimum????? $7980.00 plus any tax???

Curious


John
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
BigB 4
Popular Topics(Views)
266,207 Are you busy
201,028 Re: Forum
189,724 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3