Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Ironic that the "Sunshine State" is lite on solar??


John
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
The government subsidies dried up


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
We average 2-3 solar permit apps a week.

The commercial jobs have almost died. I have one (1) in the last 9 months.


John
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
What is the subsidy there?

Florida just put a few bucks in the subsidy pot in January and it was gone in less than 2 hours.


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Greg:
Sorry to say, I have no clue. We just inspect.


John
Joined: Jun 2004
Posts: 613
S
Member
I've seen some line side connections for Solar PV in residential 100 & 200 amp service panels ahead of the Main on the SE conductors. IMO it is sloppy and dangerous.
Typically you only have a short section of SE wiring that connects to the Main. Now you add additional un-fused SE conductors to that panel that workers/homeowners must be careful of. It would be safer to add a J-box between the meter and the main to splice the SE cable.

Now under the new rule 705.31 in 2014 you can run those un-fused SE conductors up to 10 feet in the building...which conflicts with 230.70(A)(1) which was to limit the length of un-fused SE conductors inside a building.

I think something should be written to prohibit those Line Side Connections inside a Panel...at least in the homeowner environment.

705.31 should be removed...IMO


Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
I agree. I was surprised when John pointed it out to me. I thought we were trying to get away from excessive amounts of SE inside the house.
I smell solar contractors getting a short cut in the code to make their bids less. I guess I have to go look at the ROP and see where this came from.


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Guys:
I agree with you on the 'unprotected' tap from the service conductors to the solar AC disconnect, being a possible safety issue for those unfamiliar with solar grid tie.

Hence the 'both line & load sides of this disco may be HOT'

As to length, my inspector and I use the 'same' as service conductors practice. We are still '11 NEC.

FYI, I am not a 'lover' of the line tap; however I have to accept it IF it is compliant.


John
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
I understand that if it is code, we are stuck with it but the breaker on the load end of this solar tap is still a service disconnect. If this wire starts getting very long, you have to ask if the disconnects are grouped.


Greg Fretwell
Joined: Jun 2004
Posts: 613
S
Member
Originally Posted by gfretwell
If this wire starts getting very long, you have to ask if the disconnects are grouped.


Some AHJ's don't consider it a "Service Disconnect"...they consider it a "PV Disconnect" and therefore grouping is not required.

Placards denoting each other would be installed at both locations of equipment if not grouped.

I disagree and prefer grouping like you.

Last edited by shortcircuit; 01/20/15 06:43 PM.