#214637 12/30/14 03:35 AM
Joined: Feb 2006
Posts: 78
L
Member
This is a existing 200 amp service that had a 1 1/2 metal water pipe that was being used as the grounding electrode with (2)5/8 ground rods with # 6 wire as a supplemental electrode it is a block building with no steel. The water pipe is being replaced with pvc what is required with the GEC now that there is no water pipe only the ground rods that has a side walk over them.

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Apr 2002
Posts: 7,296
Likes: 5
Member
lite bulb:

"250.50 Grounding Electrode System. All grounding electrodes
as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bonded
together to form the grounding electrode system. Where
none of these grounding electrodes exist, one or more of
the grounding electrodes specified in 250.52(A)(4) through
(A)(8) shall be installed and used."

Based on the above, the ground rods are it!

You may want to consider checking the integrity of the existing rods. You may also install another of the GEs, and/or check with your local AHJ.

Based on the letter of 250.50, the rods are all that is required, lacking any other available item.



John
Joined: Feb 2006
Posts: 78
L
Member
They did put 1 1/2 copper back in to replace the main and extended it 3' above the floor then they replaced the overhead copper with pvc then tied back to the existing copper. I was able to tie back to the main water line that was replaced, now they had 3/0 copper run as the GEC to a buss bar and made taps off of that to a SDS and the main. Off of that tap I need to ground the water pipe that was isolated by the pvc and a copper air compressor line, what size wire is needed.

Joined: Jul 2004
Posts: 9,687
Likes: 10
G
Member
You use 250.66 to bond water lines. Other piping systems can be bonded with a wire sized to 250.122 and the circuit "likely to energize" the pipe. Typically on things like compressor piping, you could use the EGC to the compressor.
(250.104(B))

At my house the shop air line is bonded with a #8 solid but that is what I had handy. wink


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Top Posters(30 Days)
LarryC 2
NORCAL 2
Popular Topics(Views)
291,225 Are you busy
223,728 Re: Forum
209,158 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5