Single Pole Control Switch On 240-v Motor #214573 12/22/14 02:42 PM
Joined: Dec 2014
Posts: 2
0
02vito Offline OP
New Member
Installed a 20-a, 240-v, single-phase, dedicated branch circuit for an automotive lift.

The lift-installation instructions required that the lift-motor supply voltage (under load)and current be measured and recorded.

In doing this, we noticed that the lift-motor control switch is only a single-pole device. Other lifts we have worked on have had 2-pole switches.

We were surprised that a nationally-known, ETL-listed lift would use a single-pole switch on a 240-v device. Our local electrical inspector was also surprised when we informed him of what we found.

I'm wondering what others are seeing in this type application. I don't recall ever seeing a 240-v device operated from a single-pole control.

2017 / 2014 NEC & Related Books and Study Guides
Re: Single Pole Control Switch On 240-v Motor [Re: 02vito] #214575 12/22/14 03:38 PM
Joined: Jul 2004
Posts: 9,389
G
gfretwell Offline
Member
You can use single pole "control" but you still need a 2 pole disconnect.

Quote
430.84 Need Not Open All Conductors.
The controller shall not be required to open all conductors to the motor.
Exception: Where the controller serves also as a disconnecting means, it shall open all ungrounded conductors to the motor as provided in 430.111.


Greg Fretwell
Re: Single Pole Control Switch On 240-v Motor [Re: 02vito] #214582 12/23/14 03:49 AM
Joined: Sep 2002
Posts: 884
N
NORCAL Offline
Member
HVAC equipment uses single pole contactors for 208-240V units & 2 pole ones for 3 units all the time.

As the code section quoted in the previous post shows, it's quite code compliant, but means any electrician needs to be on their toes & trust nothing.

Re: Single Pole Control Switch On 240-v Motor [Re: 02vito] #214603 12/24/14 03:45 PM
Joined: Dec 2014
Posts: 2
0
02vito Offline OP
New Member
Thank you both for your responses.

The circuit in question has of course a 2-pole breaker. The lift was furnished with a pigtail and twist-lock plug, so that serves as the local disconnect.

Most of my experience is in the power industry, and at the utility where I worked, we always used control devices that broke all hot circuit legs.

Re: Single Pole Control Switch On 240-v Motor [Re: 02vito] #214607 12/24/14 10:17 PM
Joined: Jul 2004
Posts: 9,389
G
gfretwell Offline
Member
Breaking all ungrounded legs is actually pretty uncommon when they use solid state switching for controls.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 233
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 11
Popular Topics(Views)
258,518 Are you busy
194,118 Re: Forum
183,620 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3