Joined: Dec 2014
Posts: 2
0
02vito Offline OP
New Member
Installed a 20-a, 240-v, single-phase, dedicated branch circuit for an automotive lift.

The lift-installation instructions required that the lift-motor supply voltage (under load)and current be measured and recorded.

In doing this, we noticed that the lift-motor control switch is only a single-pole device. Other lifts we have worked on have had 2-pole switches.

We were surprised that a nationally-known, ETL-listed lift would use a single-pole switch on a 240-v device. Our local electrical inspector was also surprised when we informed him of what we found.

I'm wondering what others are seeing in this type application. I don't recall ever seeing a 240-v device operated from a single-pole control.

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
You can use single pole "control" but you still need a 2 pole disconnect.

Quote
430.84 Need Not Open All Conductors.
The controller shall not be required to open all conductors to the motor.
Exception: Where the controller serves also as a disconnecting means, it shall open all ungrounded conductors to the motor as provided in 430.111.


Greg Fretwell
Joined: Sep 2002
Posts: 931
Likes: 1
N
Member
HVAC equipment uses single pole contactors for 208-240V units & 2 pole ones for 3 units all the time.

As the code section quoted in the previous post shows, it's quite code compliant, but means any electrician needs to be on their toes & trust nothing.

Joined: Dec 2014
Posts: 2
0
02vito Offline OP
New Member
Thank you both for your responses.

The circuit in question has of course a 2-pole breaker. The lift was furnished with a pigtail and twist-lock plug, so that serves as the local disconnect.

Most of my experience is in the power industry, and at the utility where I worked, we always used control devices that broke all hot circuit legs.

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
Breaking all ungrounded legs is actually pretty uncommon when they use solid state switching for controls.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Top Posters(30 Days)
triple 3
BigB 3
Popular Topics(Views)
303,153 Are you busy
232,168 Re: Forum
216,901 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5