The OP said his only electrode was 2 rods.


Greg Fretwell
Horizontal Ad
Joined: Feb 2006
Posts: 78
L
Member
Thanks for all the input and your help Guys. It just gets confusing on what to do when you have no building steel to use as a grid. Still not 100% on what to do.

Last edited by lite bulb; 11/21/14 04:49 AM.
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
You've got two grounding issues to contend with- fault clearing and bonding to the building ground.

Faults are cleared by current flowing through that fat green wire you pull in with your feed. At the service, the ground buss is bonded to the neutral buss, to return 'utility' fault current to the utility's transformer over their neutral.

What about transformers? Well, the ground /neutral bond you make at your first overcurrent device after the transformer performs the same function for any 'lost' transformer secondary current.

Yet, the all of your services need to also be tied into the building's ground system. This system- the Ufer, ground rod, whatever - is best thought of as being there for lightning, though that's a bit overly simplified. What matters is that you don't want one end of the building to be at a different ground potential than the other end.

We keep this from happening by tying all our ground rods, Ufers, etc., together. If you do not have serious building steel - not even bar joists holding up the roof or a concrete slab - then you're stuck with running a ground wire back all the way to the existing ground rods.

Joined: Jul 2004
Posts: 10,024
Likes: 37
G
Member
If you want to look just like the handbook, connect a 250.66 sized jumper from each transformer to the 2/0 grounding electrode conductor and connect them with split bolts.

[Linked Image from gfretwell.com]


Greg Fretwell
Joined: Feb 2006
Posts: 78
L
Member
The 5 kva control transformer is being fed from the mcc panel with two #12 and a ground on a 10 amp fuse, its leaving the mcc with grounding type sealtight, and returning to the mcc with the same type sealtight supping one 20 amp fuse to fed the computer,and one 20 amp fuse for printers. Do I still need grounding bushing if so what size wire, and do I need a ground back from xo to the main ground bar in the mcc, bonding xo in the transformer with #8. Also the main bonding will be done on a 2"x1/4 buss bar, can the buss be mounted with spacers on 3/4 plywood.

Last edited by lite bulb; 11/24/14 10:20 PM.
Joined: Feb 2006
Posts: 78
L
Member
What is the smallest neutral I can use on this service, no 277 volt load just useing the neutral up to the first disconnect.

Joined: Jun 2004
Posts: 613
S
Member
Can't be smaller than the required GEC...

Horizontal Ad
Joined: Feb 2006
Posts: 78
L
Member
The 5 kva control transformer is being fed from the mcc panel with two #12 and a ground on a 10 amp fuse, its leaving the mcc with grounding type sealtight, and returning to the mcc with the same type sealtight supplying one 20 amp fuse to fed the computer,and one 20 amp fuse for printers. Do I still need grounding bushing if so what size wire, and do I need a ground back from xo to the main ground bar in the mcc that is grounded back to the main panel, bonding xo in the transformer with #8 back to the gec.

Joined: Dec 2000
Posts: 4,293
Member
Originally Posted by gfretwell
If you want to look just like the handbook, connect a 250.66 sized jumper from each transformer to the 2/0 grounding electrode conductor and connect them with split bolts.


Isn't an exothermic weld or a non-reversible crimp required instead of split bolts?

Joined: Jul 2004
Posts: 10,024
Likes: 37
G
Member
250.30(A)(4)(c) says

Quote
(c) Connections. All tap connections to the common grounding electrode conductor shall be made at an accessible location by one of the following methods:
(1) A listed connector.


Greg Fretwell
Page 2 of 3 1 2 3

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Top Posters(30 Days)
Trumpy 5
davey 1
Popular Topics(Views)
550,222 Are you busy
424,859 Re: Forum
396,174 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5