Joined: Sep 2014
Posts: 4
D
dwhite Offline OP
New Member
I thought junction boxes mounted on a floor had to have the top flush with the floor. However, a box, along with conduit going over to, and up one wall, was mounted on top of the floor in the classroom I work in in Chicago. It is in a corner of the room about 8" from one wall, and 16" from the other. It is about 2" in height above the floor. I'm wondering if I am mistaken about a floor box needing to be flush, or if there are exceptions I am unaware of.


Horizontal Ad
Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
Floor boxes need to be listed as floor boxes. Then they have to be installed per instructions. That should get you what you need.


Greg Fretwell
Joined: Sep 2014
Posts: 6
F
New Member
The term "floor box" is usually reserved for a box with a receptacle installed face up. You pose (possibly) a different dilemma, a "junction" box which would not have a device installed, does not have the same restrictions. The only "electrical" issue would be if it were subject to physical damage as determined by whoever inspected the work. Other than that, there may be safety implications.

Joined: Sep 2014
Posts: 4
D
dwhite Offline OP
New Member
Thank you.

Joined: Sep 2014
Posts: 4
D
dwhite Offline OP
New Member
Yes - this is a junction box with conduit going over to the wall from the box. There is no receptacle. Based on the distances from the two walls, it seems like a safety hazard. The only reference I could find was that floor boxes had to be flush with the top of the floor, but maybe there are exceptions for J-boxes.

Joined: Apr 2002
Posts: 7,412
Likes: 8
Member
As 'Fiver' said, if it was inspected, the AHJ must have been OK with it.

It may be for a counter, desk, or some other item that is not installed.

As it sounds like it's in a corner, it probably is not considered a 'trip' hazard.

Just for info, what type of classroom,??



Last edited by HotLine1; 09/29/14 10:10 PM.

John
Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
Yup Fiver is right. I missed the "receptacles" in 317.17(C)


Greg Fretwell
Horizontal Ad
Joined: Sep 2014
Posts: 4
D
dwhite Offline OP
New Member
It is in an elementary school classroom and has not yet been inspected. It is not for a counter or desk, and nothing will be installed over it. It is in a corner and, as mentioned above, it is about 16" from one wall and 8" from the other.

Joined: Apr 2002
Posts: 7,412
Likes: 8
Member
OK, if I was the inspector, 'Why is it there" and if no good reason..."Remove it"

Trip hazard, subject to physical damage, etc.



John
Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
Does your state have a separate code for schools? In Florida they have the SREF codes that deal particularly with buildings in the school system. You might get something there,


Greg Fretwell

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
352,586 Are you busy
276,310 Re: Forum
255,750 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5