Code for Junction Box mounted on Floor #214073
09/28/14 10:54 PM
09/28/14 10:54 PM
D
dwhite  Offline OP
New Member
Joined: Sep 2014
Posts: 4
IL
I thought junction boxes mounted on a floor had to have the top flush with the floor. However, a box, along with conduit going over to, and up one wall, was mounted on top of the floor in the classroom I work in in Chicago. It is in a corner of the room about 8" from one wall, and 16" from the other. It is about 2" in height above the floor. I'm wondering if I am mistaken about a floor box needing to be flush, or if there are exceptions I am unaware of.


2017 / 2014 NEC & Related Books and Study Guides
Re: Code for Junction Box mounted on Floor [Re: dwhite] #214075
09/29/14 01:32 AM
09/29/14 01:32 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
Floor boxes need to be listed as floor boxes. Then they have to be installed per instructions. That should get you what you need.


Greg Fretwell
Re: Code for Junction Box mounted on Floor [Re: dwhite] #214077
09/29/14 06:26 PM
09/29/14 06:26 PM
F
Fiver  Offline
New Member
Joined: Sep 2014
Posts: 6
United States of America
The term "floor box" is usually reserved for a box with a receptacle installed face up. You pose (possibly) a different dilemma, a "junction" box which would not have a device installed, does not have the same restrictions. The only "electrical" issue would be if it were subject to physical damage as determined by whoever inspected the work. Other than that, there may be safety implications.

Re: Code for Junction Box mounted on Floor [Re: gfretwell] #214078
09/29/14 08:35 PM
09/29/14 08:35 PM
D
dwhite  Offline OP
New Member
Joined: Sep 2014
Posts: 4
IL
Thank you.

Re: Code for Junction Box mounted on Floor [Re: Fiver] #214079
09/29/14 08:39 PM
09/29/14 08:39 PM
D
dwhite  Offline OP
New Member
Joined: Sep 2014
Posts: 4
IL
Yes - this is a junction box with conduit going over to the wall from the box. There is no receptacle. Based on the distances from the two walls, it seems like a safety hazard. The only reference I could find was that floor boxes had to be flush with the top of the floor, but maybe there are exceptions for J-boxes.

Re: Code for Junction Box mounted on Floor [Re: dwhite] #214080
09/29/14 09:08 PM
09/29/14 09:08 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,926
Brick, NJ USA
As 'Fiver' said, if it was inspected, the AHJ must have been OK with it.

It may be for a counter, desk, or some other item that is not installed.

As it sounds like it's in a corner, it probably is not considered a 'trip' hazard.

Just for info, what type of classroom,??



Last edited by HotLine1; 09/29/14 09:10 PM.

John
Re: Code for Junction Box mounted on Floor [Re: dwhite] #214083
09/29/14 11:57 PM
09/29/14 11:57 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
Yup Fiver is right. I missed the "receptacles" in 317.17(C)


Greg Fretwell
Re: Code for Junction Box mounted on Floor [Re: HotLine1] #214120
10/06/14 10:34 PM
10/06/14 10:34 PM
D
dwhite  Offline OP
New Member
Joined: Sep 2014
Posts: 4
IL
It is in an elementary school classroom and has not yet been inspected. It is not for a counter or desk, and nothing will be installed over it. It is in a corner and, as mentioned above, it is about 16" from one wall and 8" from the other.

Re: Code for Junction Box mounted on Floor [Re: dwhite] #214121
10/07/14 09:44 AM
10/07/14 09:44 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,926
Brick, NJ USA
OK, if I was the inspector, 'Why is it there" and if no good reason..."Remove it"

Trip hazard, subject to physical damage, etc.



John
Re: Code for Junction Box mounted on Floor [Re: dwhite] #214122
10/07/14 12:10 PM
10/07/14 12:10 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
Does your state have a separate code for schools? In Florida they have the SREF codes that deal particularly with buildings in the school system. You might get something there,


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
244,037 Are you busy
181,031 Re: Forum
171,276 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.003s) Memory: 1.0104 MB (Peak: 1.1919 MB) Zlib enabled. Server Time: 2018-02-21 11:25:59 UTC