|
0 members (),
105
guests, and
27
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
I seem to remember that in the NEC it said that the grounded conductor (neutral) had to originate from the same panel as the ungrounded conductor. Has that been removed, or am I just wrong? I'm thinking there was an issue with the "Gentran" box used with portable generators. or possibly this 8 circuit panel that includes the transfer switch made by Generac. Thanks in advance.
George Little
|
|
|
|
Joined: Jul 2004
Posts: 10,005 Likes: 37
Member
|
As far as I know, the grounded conductor originates in the service disconnect enclosure where the main bonding jumper lands. Beyond that it just needs to be run in the same cable or raceway as the ungrounded conductors.
Maybe I don't understand the question.
Greg Fretwell
|
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
I guess I didn't explain it very well. I'm talking about a situation where we have the ungrounded conductors originating in one panel and the grounded conductors being in another panel like you could end up with using a generator and a transfer switch.
300.3(B) kinda covers it but I was thinking of the situation where the neutrals are coming from a different source.
George Little
|
|
|
|
Joined: Jul 2004
Posts: 10,005 Likes: 37
Member
|
Yup that was where I was going.
Greg Fretwell
|
|
|
|
Joined: Jul 2004
Posts: 10,005 Likes: 37
Member
|
Where is the neutral coming from and how can they do that without violating 300.3
Greg Fretwell
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
Wouldn't 300.3(B)(4) be similar in practice to the way a gen-tran transfer switch is installed?
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
With those gen-tran switches and all the AFCI breakers required...you can't use them and keep the AFCI protection while on generator.
|
|
|
|
Joined: Jul 2004
Posts: 10,005 Likes: 37
Member
|
Looking at the GenTran installation guide, it does appear that there is a neutral bus in the GenTran and they talk about installing the required GFCI/AFCI breakers in the GenTran. http://gentran.net/assets/pdfs/EncoreInstall.pdfI also saw another smaller GenTran that looks like it uses plug fuses. That would be troubling on a new installation. There does not seem to be any provision for xFCI https://gentran.net/assets/pdfs/oldinstall.pdf
Greg Fretwell
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
It is the smaller gen-tran switch that is most popular. It is sold in home stores also. This is the one without neutral provisions.
|
|
|
|
Joined: Jul 2004
Posts: 10,005 Likes: 37
Member
|
The Encore is the one I see listed at my local Home Depot.
If they have one that will not accommodate xFCI breakers and does not have a neutral bus, I would call it a violation, on a couple of counts. Even if they could make the case that none of the circuits served required GFCI or AFCI, I would still have trouble with the edison base fuse holders, even if they do have push button breakers in them. (like the second one in my post above)
Greg Fretwell
|
|
|
Posts: 61
Joined: August 2007
|
|
|
|
|