520-theaters #213742 07/06/14 02:16 PM
Joined: Apr 2002
Posts: 184
T
triple Offline OP
Member
Am I correct that pvc conduit is allowed for essentially all low-volt conductors in a theater (according to 520.5(A) exception and handbook commentary)? Also, would pvc be among the code-compliant wiring methods for circuit and feeder conductors below a wood floor of an old theater? A wood floor obviously is not "fire rated construction". Purhaps the existing wood floor would not meet current building code?

2017 / 2014 NEC & Related Books and Study Guides
Re: 520-theaters [Re: triple] #213743 07/06/14 06:54 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Theatres are SO touchy that you can't make your plans based upon the NEC.

You always need to touch base with the Fire Marshal.

The last theatre I worked on -- quite a while back -- the FM restricted PVC usage to below slab. The transition to EMT had to occur dang near flush with the slab.

PVC decays into cyanide gas and soot during partial combustion. Consequently many FM will not tolerate PVC since this result can be triggered by fires not started by the Low Voltage conductors.

Don't be surprised if plenum rated cables become necessary.


Tesla
Re: 520-theaters [Re: triple] #213744 07/06/14 07:09 PM
Joined: Apr 2002
Posts: 184
T
triple Offline OP
Member
In my personal opinion, pvc should not be allowed no matter what. However, the NEC , the NEC handbook, and a third-party handbook I have, all state that the rule does not directly apply to the communication, A/V, and fire alarm wiring. For these systems we are instructed to use their respected code articles. Those individual code articles simply say to use chapters 1-4 (specifically 3 of course). Obviously, different cities/municipalities can make up whatever rules they see fit. At present, I am only interested in national code. Thank you for your response Tesla.

Re: 520-theaters [Re: triple] #213748 07/06/14 10:11 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
I agree with Tesla. In any "assembly" the fire code official is the king of the hill. You can meet the NEC and still not make them happy.


Greg Fretwell
Re: 520-theaters [Re: triple] #213750 07/06/14 10:53 PM
Joined: Apr 2002
Posts: 7,105
HotLine1 Offline
Member
Agree with Tesla & Greg on the Fire Official.

Between the Building Codes and NFPA Fire Codes, any exposed PVC is not allowed. Products of combustion; flammability, flame spread, etc.


John
Re: 520-theaters [Re: triple] #213752 07/07/14 09:34 AM
Joined: Apr 2002
Posts: 184
T
triple Offline OP
Member
No conduit is exposed, pvc or otherwise.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
GeneSF 7
Popular Topics(Views)
257,954 Are you busy
193,679 Re: Forum
183,292 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3