520-theaters #213742
07/06/14 01:16 PM
07/06/14 01:16 PM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
Am I correct that pvc conduit is allowed for essentially all low-volt conductors in a theater (according to 520.5(A) exception and handbook commentary)? Also, would pvc be among the code-compliant wiring methods for circuit and feeder conductors below a wood floor of an old theater? A wood floor obviously is not "fire rated construction". Purhaps the existing wood floor would not meet current building code?

2017 / 2014 NEC & Related Books and Study Guides
Re: 520-theaters [Re: triple] #213743
07/06/14 05:54 PM
07/06/14 05:54 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Theatres are SO touchy that you can't make your plans based upon the NEC.

You always need to touch base with the Fire Marshal.

The last theatre I worked on -- quite a while back -- the FM restricted PVC usage to below slab. The transition to EMT had to occur dang near flush with the slab.

PVC decays into cyanide gas and soot during partial combustion. Consequently many FM will not tolerate PVC since this result can be triggered by fires not started by the Low Voltage conductors.

Don't be surprised if plenum rated cables become necessary.


Tesla
Re: 520-theaters [Re: triple] #213744
07/06/14 06:09 PM
07/06/14 06:09 PM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
In my personal opinion, pvc should not be allowed no matter what. However, the NEC , the NEC handbook, and a third-party handbook I have, all state that the rule does not directly apply to the communication, A/V, and fire alarm wiring. For these systems we are instructed to use their respected code articles. Those individual code articles simply say to use chapters 1-4 (specifically 3 of course). Obviously, different cities/municipalities can make up whatever rules they see fit. At present, I am only interested in national code. Thank you for your response Tesla.

Re: 520-theaters [Re: triple] #213748
07/06/14 09:11 PM
07/06/14 09:11 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,302
Estero,Fl,usa
I agree with Tesla. In any "assembly" the fire code official is the king of the hill. You can meet the NEC and still not make them happy.


Greg Fretwell
Re: 520-theaters [Re: triple] #213750
07/06/14 09:53 PM
07/06/14 09:53 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
Agree with Tesla & Greg on the Fire Official.

Between the Building Codes and NFPA Fire Codes, any exposed PVC is not allowed. Products of combustion; flammability, flame spread, etc.


John
Re: 520-theaters [Re: triple] #213752
07/07/14 08:34 AM
07/07/14 08:34 AM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
No conduit is exposed, pvc or otherwise.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,518 Are you busy
188,690 Re: Forum
178,391 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.003s) Memory: 0.9770 MB (Peak: 1.1261 MB) Zlib enabled. Server Time: 2018-11-16 23:14:32 UTC