MC cable #213589 06/06/14 10:38 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
I'm looking at an old 2005 code book, and it gives the qualifications for MC cable to be used in wet locations. The location I'm figuring is just damp, not actually wet. It says the conductors are to be listed for wet locations, covering to be impervious to moisture etc.. Does the MC cable that is normally bought, say at Lowes, fit these criteria? Thanks

Work Gear for Electricians and the Trades
Re: MC cable [Re: sparkync] #213590 06/07/14 12:15 AM
Joined: Dec 2000
Posts: 4,280
electure Offline
Member

There's a type of MC cable that has a PVC jacket on top of the armor, Southwire calls it Parking Lot/Deck Cable.

Special connectors must be used with it, as well. The connectors have a gland nut, much like the gland nut on a cord grip.

From 2011 NEC, 330.10(A) :

(11) In wet locations where any of the following conditions are met:

a. The metallic covering is impervious to moisture.
b. A moisture-impervious jacket is provided under
the metal covering.
c. The insulated conductors under the metallic covering
are listed for use in wet locations, and a corrosion resistant jacket is provided over the metallic sheath.


Normal MC does not fit the bill frown




Re: MC cable [Re: sparkync] #213591 06/07/14 01:06 AM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
Most aluminum jacket MC is listed "wet", simply because they use a wet location conductor inside the jacket.
(per (c) above).



Greg Fretwell
Re: MC cable [Re: sparkync] #213592 06/07/14 09:31 AM
Joined: Dec 2000
Posts: 4,280
electure Offline
Member
Greg, are you sure?

(c) also states "and a corrosion resistant jacket is provided over the metallic sheath."


Both AFC and Southwire say their aluminum armored MC is listed for "Dry use only"



Re: MC cable [Re: sparkync] #213593 06/07/14 12:48 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
This is the box I have in the garage.

[Linked Image]


Greg Fretwell
Re: MC cable [Re: sparkync] #213594 06/07/14 02:29 PM
Joined: Dec 2000
Posts: 4,280
electure Offline
Member
From the 2005NEC:

(11) In wet locations where any of the following conditions are met:
a. The metallic covering is impervious to moisture.
b. A lead sheath or moisture-impervious jacket is provided under the metal covering.
c. The insulated conductors under the metallic covering are listed for use in wet locations.

The code Changed in 2008 it's present verbiage, and also first prohibited FMC in wet locations, too.

Could it be you bought cable pre-2008?







Re: MC cable [Re: sparkync] #213595 06/07/14 07:01 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
It would appear the committee is trying to stop the use of MC and Greenfield as HVAC condenser whips.

In commercial work they have long been considered unacceptable.

Yet you see them all over town, hereabouts, powering up HVAC condensers -- pad mounted -- residential.

With this rule change, Sealtite or PVC coated MC becomes required.

Since I can't point to any fire risk issues, it would appear to be a code change motivated by the NEMA players.



Tesla
Re: MC cable [Re: sparkync] #213596 06/07/14 10:26 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
I certainly see no issue with the cable above.
The inside of a raceway is still a wet location if it is outside and THWN is a wet rated conductor. What difference does it make if the rain is getting into the MC/FMC? Is it any wetter than a buried raceway is filled with water?

I have seen plenty of regular aluminum MC outside. You just need the cables arranged so they don't fill the boxes with water (typically bottom entry)


Greg Fretwell
Re: MC cable [Re: sparkync] #213601 06/08/14 01:40 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
There's never really been an issue with MC itself in a wet / outdoor location. You're doing just fine until you get to the end of the cable.

Why? Because every MC connector I've ever seen has been marked as for 'dry locations only.' There's the problem.

Were it not for the price of the (weather-tight) fittings, I suspect we'd see a lot of UF used as HVAC whips.

------------------------

As I learned the trade, the only material considered for such whips was metal-lined "Sealtite." I will admit that there is still a role that only such a method can meet.

Yet, I wonder if we're trying too hard to be 'perfect?' For the applications we're discussing, we're using "normal" 20- or 30-amp 120 power. Even the use of 240 in residential air conditioning is becoming rare. It seems a natural application for a less elaborate method - even (gasp!) a cord and plug.

Frankly, I'd have greater faith in a cord & plug than I currently have in the typical installation, where the flex is falling out of its' connectors and the connectors are hung on a disconnect that seems to be made of foil, and is usually improperly mounted.(How often do you see one of the mounting holes wide open to the weather?)

Re: MC cable [Re: sparkync] #213604 06/08/14 03:24 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
I never understood why you were not allowed to glue LFNC into a male adapter (except that Carlon would lose a couple bucks)

They do let you glue up ENT.


Greg Fretwell
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
GeneSF 7
Popular Topics(Views)
257,954 Are you busy
193,679 Re: Forum
183,292 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3