70E quandry #213184
03/28/14 12:09 AM
03/28/14 12:09 AM
T
TheGreatSparkalini  Offline OP
New Member
Joined: Aug 2005
Posts: 4
Sanford, Maine USA
I need to know if my training is lacking or if a concern from a manager has no merit. The manager is insisting that 30 cal flash gear is needed to reset a tripped 3000A 480 VAC main breaker. The breaker and all the gear around it is fully enclosed. The Approach is 26.5 ft and limited is 3.6 feet. Am I wrong to assume that these barriers only apply with the covers open. I definitely will need to review 70E to set myself or the manager straight. I appreciate his zeal to keep us safe but this seems extreme. What do you all think?

Work Gear for Electricians and the Trades
Re: 70E quandry [Re: TheGreatSparkalini] #213187
03/28/14 01:01 PM
03/28/14 01:01 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
If the covers are all on, no PPE is required, much less a 30 cal suit.

Ask the manager if he puts on flash gear to reset one of his breakers at home

rolleyes

Re: 70E quandry [Re: TheGreatSparkalini] #213188
03/28/14 01:42 PM
03/28/14 01:42 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
Is there any concerns over what tripped the 3000 amp main?

Hopefully it was the GF


John
Re: 70E quandry [Re: TheGreatSparkalini] #213192
03/28/14 04:10 PM
03/28/14 04:10 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by TheGreatSparkalini
Am I wrong to assume that these barriers only apply with the covers open.


Appropriate PPE is always required, regardless of covers being present or absent.

closed covers mitigate any possible shock incident, and they probably do help in the prevention of an AF occurrence, but the do nothing to lower the amount of incident energy.

While I might judge the 'normal operation' of a 3000A breaker between open and closed as having a low risk of an AF occurring, there is no way I would 'reset' a tripped breaker without PPE based on the available incident energy.

Re: 70E quandry [Re: electure] #213193
03/28/14 04:13 PM
03/28/14 04:13 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by electure
If the covers are all on, no PPE is required, much less a 30 cal suit.


The PPE requirements need to be part of the company's Electrical Safe Work Practice program.

Re: 70E quandry [Re: JBD] #213195
03/28/14 04:22 PM
03/28/14 04:22 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Quote
The PPE requirements need to be part of the company's Electrical Safe Work Practice program.


So the outside consultant with a vested interest in separating you from your money, will specify the most conservative interpretation of the 70E rules in order to validate their cost to the company. Meanwhile you will need PPE to plug in a vacuum cleaner in the office spaces.

Re: 70E quandry [Re: TheGreatSparkalini] #213196
03/28/14 06:48 PM
03/28/14 06:48 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
Bob,
Refer the manager to Table 130.7(C)(15)(a) of 70E,
available @
http://www.depts.ttu.edu/opmanual/OP60.14B.pdf

It lists the Hazard/Risk Category Classifications.

Panelboards or Switchboards Rated >240 V and up to 600 V (with molded case or insulated case breakers)

CB or fused switch operation with covers on

Hazard Risk = 0
______________________________________________________

600 V Class Switchgear (with power circuit breakers or fused switches)

CB or fused switch operation with covers on

Hazard Risk = 0





Re: 70E quandry [Re: LarryC] #213202
03/29/14 01:29 PM
03/29/14 01:29 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by LarryC
So the outside consultant with a vested interest in separating you from your money, will specify the most conservative interpretation of the 70E rules in order to validate their cost to the company. Meanwhile you will need PPE to plug in a vacuum cleaner in the office spaces.


If the people doing your analysis are the same ones that are selling you your PPE, you probably have a point.

My point is; it is not a requirement of NFPA70E that you employ any more PPE than is necessary to perform the task.

The typical AF study says how bad things could be (the hazard), not how likely they are to occur(the risk).

70E clearly says that the risk must be analyzed as well as the danger. The is partly why their 'task tables' result in a Hazard Risk Category instead of simply cal/cm^2.

Re: 70E quandry [Re: electure] #213203
03/29/14 01:33 PM
03/29/14 01:33 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by electure
Bob,
Refer the manager to Table 130.7(C)(15)(a) of 70E....


And make sure that all of the conditions (fault current, opening times, and regular maintenance) are met.

Re: 70E quandry [Re: TheGreatSparkalini] #213208
03/29/14 02:48 PM
03/29/14 02:48 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,302
Estero,Fl,usa
This is like most things "safety" related. If it is worth doing, it is worth over doing.

You only have to look ad lead paint and asbestos abatement this in action. Someone dug up some sewer pipe here in a road expansion project that *might* have had some asbestos in it and instead of some reasonable response, they shut down the project for months, hauled about 100 yards of dirt for "safe disposal" and treated the pipe like it was plutonium. Everyone involved was punished in some way and the contractor went bankrupt. An overpass took years and many extra millions to complete.


Greg Fretwell
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,513 Are you busy
188,688 Re: Forum
178,391 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 16 (0.004s) Memory: 1.0273 MB (Peak: 1.2045 MB) Zlib enabled. Server Time: 2018-11-16 20:13:00 UTC