Looking at pulling 3-4/0 aluminum XHHW conductors approx 90 feet with four long 90s (sweeps)in 2" IMC. Is this doable using 2" IMC and 2 guys? Actually we could put the end sweep together last which would reduce it to 3 90s and about 80 feet.
BigB #211435 10/11/13 11:35 PM
With no grounding conductor?
By code the conduit run should be installed first. Trying to spin a sweep on a pipe can damage the conductors. I don't have my NEC handy but I'm pretty sure you can pull the 4/0 in especially if they are compact AL conductors
BigB #211436 10/12/13 09:58 AM
twh Offline
There are a lot of variables that you aren't sharing. Pulling up or down, feeding up or down, space to stretch cables out on the feed end, locations of the 90s, the size of the guys etc.
I think it's cheaper to have one guy stand around doing nothing than to have a crew wait for a couple hours while you find help.
BigB #211437 10/12/13 12:12 PM
BigB Offline OP
first 90 under panel into ground then 12 feet laterally to second 90 coming up outside patio wall and into third 90 to change directions 90 degrees, then 70 feet along wall to last 90 which will sweep up into the service mast. Average guys, not weak, not Charles Atlases either.
BigB #211438 10/12/13 01:32 PM
Lube. Lotsa lube
BigB #211439 10/12/13 02:22 PM
twh Offline
3 guys.
2 guys on the feed end to start. One guy pulls slack in the cable and the other pushes and lubes. "Pulling wire" is misleading. Half the job is pushing the wire.
After halfway, move one guy to the other end to help pull. Pulling up makes it hard to have more than two guys on the rope, anyway.
Don't forget lotsa rags to go with the lotsa lube.
If you try with two guys, you might need to pull one 90 off and tie the rope to something to give you more leverage - like a 2x4 and a fulcrum or maybe even a truck. It might go okay, but it might suck for many hours.
It would be nice to feed from the end closest to the most 90s. I think lubed cable slides around a 90 easier than a dry rope.
BigB #211440 10/12/13 08:00 PM
You could put a conduit body somewhere along the way to break up the pull. Maybe an LB at the "change of direction" after you get up out of the ground.
Think about where you get the best place to work.
BigB #211442 10/13/13 02:07 PM
BigB Offline OP
No conduit bodies before the meter are allowed by the POCO. I decided to go with 2.5" pipe.
BigB #211443 10/13/13 02:33 PM
That's gonna be a jump on material price. Anything over 2" in size, thei cost goes up expotentially
Is there a way to use an ordinary come-along or winch of some type?
You can use a choker on the rope a what is called a French prusik. It works on the same principle as a choker but you use a small peice of rope. It's easier on the rope than a choker can be
The link is how to use a prusik. It's a variant of the one I use but it works and simple to use
http://m.youtube.com/watch?v=u0YxU5C_KrQ
With some type of winch or even with block and tackle one person can feed while one person pulls even with the biggest and longest pulls
BigB Offline OP
Yes I have a come-along, a high lift jack and a boat winch and I have considered using one of them.
Thanks for the link