Can I use a 600W Toggle dimmer in a 20A circuit? #211297
10/03/13 11:43 AM
10/03/13 11:43 AM
H
Hormel1144  Offline OP
New Member
Joined: Oct 2013
Posts: 1
NYC
Hello: I'd like to install a GE toggle-style dimmer in a 20A circuit. My concern is that the maximum load the dimmer is rated for in a single gang setup is 600W (it is downrated for multiple gang setups). This works out to a load capacity of 5A or less, in a circuit where the overcurrent protection will happily pass 20A before tripping; or enough to fry the device at least 4 times over. I understand that the code allows fixture pigtails to be sized to the max wattage of the fixture, regardless of the ampacity of the supply, because the maximum load on the pigtail will never be more than the fixture's maximum wattage. The issue here, however, is that the dimmer feeds into 12ga house wiring, and it is possible that in the future multiple fixtures could be attached to the leg, drawing as much as 2400w! We would then have a circuit which was not fully sized to handle the load permitted by the overcurrent protection. Wouldn't this violate the code?

2017 / 2014 NEC & Related Books and Study Guides
Re: Can I use a 600W Toggle dimmer in a 20A circuit? [Re: Hormel1144] #211309
10/03/13 09:38 PM
10/03/13 09:38 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,051
Brick, NJ USA
IMHO, your concern at the time of installation is that you do not exceed the rating of the device controling the load.

The circuit is protected by the 20 amp OCP, which is compliant.

For example; you install 6 recess fixtures with 75 watt lamps, totaling 450 watts. The load on the device is within spec, even if it is two ganged.

Some time after you do the above; someone replaces the lamps with 150 watt lamps! The dimmer takes the bullet!!

Code compliance is 'at the time of installation/inspection'. There is no crystal ball, no lady reading the future, and the NEC is not 'idiot proof'.

A 120 volt 20 amp circuit calcs to 2400 watts, max load for non-continuous, and would be compliant. Common trade practice is NOT to load any circuit to 'max'.


John
Re: Can I use a 600W Toggle dimmer in a 20A circuit? [Re: Hormel1144] #211313
10/04/13 12:30 AM
10/04/13 12:30 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,325
Estero,Fl,usa
This is an interesting question. I suspect the real answer would be if U/L added the requirement of a fusible link in the device to blow if the allowable current was exceeded but, as far as I know it is not in the listing standard.
I suspect from experience that the triac would simply short and make it a switch.
Dimmers seem to fail "on".




Greg Fretwell
Re: Can I use a 600W Toggle dimmer in a 20A circuit? [Re: Hormel1144] #211316
10/04/13 07:00 PM
10/04/13 07:00 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Ever try to find a dimmer rated for the full ampacity of a circuit? Good luck - and, if you find one, it will have a metal cover the size of a dinner plate, just to dissipate the heat.

Even most light switches are not rated for the full current- look closely, and you'll find plenty with straps stamped "10A."

It appears there has never been a requirement for a switch to be capable of anything more than controlling the intended load.

Re: Can I use a 600W Toggle dimmer in a 20A circuit? [Re: Hormel1144] #211320
10/04/13 08:38 PM
10/04/13 08:38 PM
B
BigB  Offline
Member
Joined: Mar 2004
Posts: 734
Tucson, AZ USA
This brings up a topic which is a pet peeve with me, inspectors who will try to enforce "idiot proofing". There is nothing in the code that I know of that requires us to go over the minimum requirements "in case" someone comes later and adds something. The "what ifs" could go on forever and my answer to them is whoever does the "what if" at a later date will be responsible for whatever is needed at that time.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,279 Are you busy
189,226 Re: Forum
178,915 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.005s) Memory: 0.9714 MB (Peak: 1.1130 MB) Zlib enabled. Server Time: 2018-12-18 23:24:38 UTC