ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Grounding electrodes
by gfretwell - 09/07/21 03:41 PM
Looking For Electricians in the Midlands
by Alex247 - 09/06/21 05:26 AM
Backup Generator Done Right
by timmp - 08/31/21 04:44 PM
New in the Gallery:
Now you know.
Now you know.
by Tom_Horne, September 7
February, North East Indiana
February, North East Indiana
by timmp, July 25
Who's Online Now
0 members (), 31 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#210979 08/29/13 07:23 PM
Joined: Oct 2002
Posts: 830
S
Member
I've got a permit on a detached RV garage right next to the house it belongs to, ( had to run it all in conduit). The house already has been inspected and has power. While checking on my job, I thought I would just look at the electrical panel for the house, since it is right next to the garage I will be working on. I noticed that there were no AFCI's on Bathroom recepts., microwave recept., wash machine recept., kitchen lights, garage outlets, and dishwasher and disposal multiwire circuit. It's been a while since I've wired a new house, but I was thinking that everything except maybe the baths and kitchen had to have AFCI's. Obviously I was wrong. Don't have my new code with me right now. I sort of see all the above being ok, since they are GFI protected after the first outlet, except "kitchen lights". Don't understand that one. The only one's that did have AFCI's were, Master bedroom outlets, Bedroom outlets, and living room . Any comments?? Think the inspector just missed it?

2017 / 2014 NEC & Related Books and Study Guides
sparkync #210981 08/29/13 07:58 PM
Joined: Aug 2005
Posts: 250
T
Member
We have only been required to ARc protected bedrooms and smoke detectors. Nothing else ...yet.


Shake n Bake
sparkync #210984 08/29/13 10:46 PM
Joined: Apr 2002
Posts: 7,279
Likes: 3
Member
sparkync:
This is from the 2011 NEC:

210.12 Arc-Fault Circuit-Interrupter Protection.
(A) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall
be protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.

Note that 'kitchen' is not mentioned, so the kitchen lights are not mandatory for AFCI protection.

What NEC is in effect in your area?


John
sparkync #210985 08/29/13 11:03 PM
Joined: Feb 2008
Posts: 193
S
Member
We are on 2011. Our inspectors are pretty lenient on what you need to have arc faults on. I usually end up with 7-9 breakers for a whole house on the general use recepts. I have not been failed for not having something on arc faults.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Top Posters(30 Days)
timmp 3
FGBY 2
Popular Topics(Views)
282,917 Are you busy
216,686 Re: Forum
203,109 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5