Convert 240V to 208V? #210779 08/04/13 01:11 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
Can a 240V-3ph panelbd (with a wild leg) be easily converted to 208V-3ph? (assume that any connected equipment can operate on 208V)

Work Gear for Electricians and the Trades
Re: Convert 240V to 208V? [Re: cgw] #210780 08/04/13 01:36 PM
Joined: Apr 2002
Posts: 7,215
HotLine1 Online Content
Member
Is this panel fed from the utility co? If so, then the POCO is where the modifications are started.



John
Re: Convert 240V to 208V? [Re: cgw] #210781 08/04/13 04:03 PM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
If you are just running motors it probably doesn't matter and a lot of other equipment can be jumpered t0 run 208 or 240.

Like John says, this is a PoCo option. They will need to add another transformer, probably replacing the small one you have too.
The typical center tapped delta uses a smaller transformer for the wild leg and they only use 2, leaving one side of the delta open (AKA Delta Vee)
Expect a fee for this.

I bet your transformers look like this.

[Linked Image from gfretwell.com]




Greg Fretwell
Re: Convert 240V to 208V? [Re: cgw] #210782 08/04/13 04:04 PM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
You want this
[Linked Image from gfretwell.com]


Greg Fretwell
Re: Convert 240V to 208V? [Re: cgw] #210785 08/05/13 12:02 AM
Joined: Mar 2005
Posts: 212
G
Gregtaylor Offline
Member
The direct answer to the question you actually asked is, no its not hard because its the same panel. After that, see the above answers.

Re: Convert 240V to 208V? [Re: cgw] #210789 08/05/13 05:06 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
Everything up to the panelbd will be replaced (the entire service). There is no question on the line side.
I assume (I am going over to look at it tomorrow) that only the 3 phase loads are connected to the middle bus (in this case maybe a rooftop unit - it is retail). So when it becomes 208V the middle phase will be un-balanced. In addition - the panelbd is currently the service entrance. That will no longer be the case after the change (there will be a line side main disconnect). So the neutral needs to be separated (I'm thinking out-loud). Any other considerations?

Re: Convert 240V to 208V? [Re: cgw] #210790 08/05/13 05:49 PM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
You can swap some breakers around and balance the service once you get real 3p wye in there.
You can get a head start by going in with your clamp when they are running their normal load and tagging the current on each circuit. Then you will have a starting point for the rebalance.
We used to have to do that in computer rooms sometimes because each machine might have significant single phase loads and the luck of the draw might get some unwanted imbalance.


Greg Fretwell
Re: Convert 240V to 208V? [Re: cgw] #210791 08/05/13 08:50 PM
Joined: Apr 2002
Posts: 7,215
HotLine1 Online Content
Member
Once you get an OK from the POCO, and they do their thing at the pole, you should be good to go.

You may find 2 pole, 240 volt circuits on the 'B' phase, and whatever 3 phase equipment you have on the site.

As to maintaining a balance, Gregs head start is a good plan.


John
Re: Convert 240V to 208V? [Re: cgw] #210792 08/05/13 09:10 PM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
We didn't see much in computer rooms but it usually will be the L/N loads he has to move. They are all on A/C now.


Greg Fretwell
Re: Convert 240V to 208V? [Re: cgw] #210793 08/05/13 09:18 PM
Joined: Apr 2002
Posts: 7,215
HotLine1 Online Content
Member
Over the years, I saw many panels with nothing on 'B' phase.

Most were in factorys that were vacated, and 'quick' converted to other uses. A lot of breaker blanks with 'RED LEG' written on them.


John
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,880 Are you busy
205,739 Re: Forum
193,850 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3