power factor correction #210613
07/13/13 03:32 PM
07/13/13 03:32 PM
A
ANNEMARIE  Offline OP
Member
Joined: Oct 2012
Posts: 39
DORSET UK
Hi all can anyone tell me if the uk electrical networks have power factor correction capacitors fitted at 33/11kv substation sites or are these only fitted at supergrid sites thanks in advance annemarie

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: power factor correction [Re: ANNEMARIE] #210716
07/25/13 06:41 AM
07/25/13 06:41 AM
B
boora2  Offline
Member
Joined: Jun 2012
Posts: 15
Mt Pritchard,Sydney, New South...
As I'm from Australia,a UK guy would be the best to answer this,but I seem to remember there is some gear at the 275kV Willsden yard to regulate the kVARS on the incoming cables to insure either one is not too badly overloaded at peak use times.

Re: power factor correction [Re: ANNEMARIE] #210735
07/27/13 02:11 AM
07/27/13 02:11 AM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,713
Anaheim, CA. USA
If the UK's Utility Providers have protocols similar to the Utility Providers here in USA
(more precisely, the "EUSERC-Related" Utilities of the Western / Pacific States),
there will be KVAR Correcting Capacitor Banks at the Distribution Yards, and at specific locations on the Distribution Feeder Circuits.

Primary Distribution Feeders are nominally 12,470Y/7200V 3PH. 4W, with some 24,000V and 34,500V Systems.
Older installs were 4160Y/2400 3PH. 4W, however these Systems are being Phased out where possible.

All Polyphase Transformer Primary connections are L-L Delta (12KV). Primary Side connections for Single Phase Pole-Mounted Transformers typically are connected L-L (12KV), but in LADWP Territory, the majority of 1 PH. Pole Mounts are L-N (2400V or 7200V).
In my area, the only L-N Single Phase Primary Terminations are for Pad-Mount Transformers.

KVAR Correction at Distribution Yards is placed on the 12KV Primary Distribution Feeders' side.
(BTW, in my area, the Sub-Transmission Circuit Voltage is 66KV, and the "Main" Transmission Circuit Voltage is 138KV)

The Yards have some PF Correction Banks constantly connected, and others connected per Time-Of-Use (TOU), via Cut-Outs.

For the remote locations (Pole Mounted Banks), there are some Permanently-Connected Banks, and some Banks which are connected via 15KV Oil-Immersed Cutout Switches.
A Time Clock, or Remote Controller opens and closes these Switches.
At each of these types of Correction Banks, there is a small (5 KVA maximum) 12KV to 120/240V Transformer, which supplies Power for the Control Equipment.

I am also interested in the UK's Primary Distribution PF Correction methods.
When you find the information, please reply!

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: power factor correction [Re: ANNEMARIE] #210742
07/27/13 03:25 PM
07/27/13 03:25 PM
A
ANNEMARIE  Offline OP
Member
Joined: Oct 2012
Posts: 39
DORSET UK
Hi thanks for the replys I think the us system is a bit different from the uk because we dont have so many xformers we tend to have 1 tranny per 150 houses im hoping that someone from a uk based poco will reply sometime soon My local supply company wont tell me anything wich is why i asked here thanks annemarie


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 98
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,239 Are you busy
189,201 Re: Forum
178,886 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.005s) Memory: 0.9615 MB (Peak: 1.0955 MB) Zlib enabled. Server Time: 2018-12-16 13:42:00 UTC