A/C Condenser working clearances #210257 06/06/13 04:21 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
Hi,
Does article 110.26 (A)(1) apply to the disconnect for the condenser unit?

or would this fall under 440.14 only required to be in sight?

I have two units with the disco mounted behind the units less than 2 feet away from the condenser..

I am thinking you need width of equipment or 30" and mounted to the left or right.

thanks

for any replies.

greg


Don't drive and TEXT! Drive now TALK LATER!
2017 / 2014 NEC & Related Books and Study Guides
Re: A/C Condenser working clearances [Re: akmaster] #210263 06/06/13 09:24 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
It is unclear.
Most AHJs do require working space in front of the condenser disconnect. The strange thing is the same guys don't seem to care about the air handler, that might be in a closet or up in the attic where is no way you can push Jim Pauley's mythical refrigerator box up to the disconnect (a rough idea of what working space looks like that he uses in his road show).


Greg Fretwell
Re: A/C Condenser working clearances [Re: akmaster] #210267 06/06/13 10:07 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
If we are talking resi, clearance issues on new construction arise when 'who is there first'. When the EC is doing trim out for finals, he mounts the discos at the location. The CUs are dropped after, and sometimes the disco is behind them, or the tall units block the disco.

When the AC line set is in & charged, guess who has to move what??

Replacement CUs usually are OK. Best comment I can add is each job has to be treated individually.

Commercial RTUs are usually no issue.

Do we live in a perfect world, No.


John
Re: A/C Condenser working clearances [Re: akmaster] #210269 06/06/13 10:50 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
The world is not even perfect at my house We put in a mini split and I wanted the condenser set near the existing one but about 3' away so I would maintain my 30" in front of the grouped disconnects with a little wiggle room to spare. I even put the pad in with the center that far away. The <expletive deleted> installer put it near the close edge of the pad!!! I ended up with about 28" as far as we could push it without running another line set.
Fortunately the inspector left his yard stick in the truck.



Greg Fretwell
Re: A/C Condenser working clearances [Re: akmaster] #210272 06/07/13 08:29 AM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
In areas that were inundated by "Sandy":

It is getting real interesting with the attempts to comply with elevation heights above the proposed new flood levels.

Replacement CUs range from the 'I don't care it staying on the grade' to 3'-8' above grade.



John
Re: A/C Condenser working clearances [Re: akmaster] #210275 06/07/13 10:54 AM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
Thank you guys for the comments..very insightful..

regards

Greg


Don't drive and TEXT! Drive now TALK LATER!
Re: A/C Condenser working clearances [Re: akmaster] #210280 06/07/13 02:09 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
Putting A/C condensers (water heaters etc) above the FEMA flood plane has been standard here for years if the finished floor of the home is FEMA compliant.
You see blocked up platforms under the condenser or water heaters in garages that are below the FEMA level.

If the house is grandfathered below FEMA, they usually ignore the water heater and AC.


Greg Fretwell
Re: A/C Condenser working clearances [Re: akmaster] #210297 06/08/13 06:11 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
John,

Do you have many Cu's up in the air on the second floor? I have them here in my town. Nothing sillier than looking out a second floor window and seeing a tiny deck with an HVAC unit sitting on it.

Re: A/C Condenser working clearances [Re: akmaster] #210302 06/09/13 01:29 AM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
Is that an indication of where FEMA says the flood plane is?
We see that at the beach where they have to build piling houses. These days the FF is about 14 feet off the sand and that is up hill from the water. They are usually 10'-12' higher than the road out front.


Greg Fretwell
Re: A/C Condenser working clearances [Re: akmaster] #210309 06/09/13 11:13 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Greg,

In one of the towns I inspect, the town gave people permission to raise their houses as long as it was the height that was governed by FEMA. The heights were different in several parts of town. Needless to say, the closer you were to the river, the higher the flood plane was. They will even allow you to build a new house in the flood plane, but there is no basement and no walls on the first floor. The water has to be allowed to flow in, under, and around the house. So all of your utility services enter in on the 2nd floor.

The water and sewer comes up out of the ground and is wrapped around with all sorts of protection from cold, inside of a hollow column.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,712 Are you busy
209,630 Re: Forum
196,972 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3