Suppose I had a large feeder running across a building (3 sets 600) and I wanted to tap the feeder with 1 set #1. Just tapping one set of the large feeder is correct and practical?
|
|
|
|
|
Joined: Jul 2007
Posts: 1,337
Member
|
Without all the technical info of what you hooking up and what the existing load,If it meets the tap requirements of article 240 and not overload the original load, and meets other applicable requirements, I don't see a problem
"Live Awesome!" - Kevin Carosa
|
|
|
|
|
Joined: Jul 2004
Posts: 10,051 Likes: 39
Member
|
I have a problem with it. The whole idea of paralleled conductors is that you are going to balance the load across the conductors equally (same size, length etc) If you unequally load one conductor, you are defeating the O/C protection. The only way I see this as legal is if you group them, make your tap and then break them out again.
I will look for a code reference
Greg Fretwell
|
|
|
|
|
Joined: Jul 2004
Posts: 10,051 Likes: 39
Member
|
This is the commentary from the handbook Where individual conductors are tapped from conductors in parallel, the tap connection must include all the conductors in parallel for that particular phase. Tapping into only one of the parallel conductor would result in unbalanced distribution of tap load current between parallel conductors, resulting in one of the conductors carrying more than its share of the load, which could cause overheating and conductor insulation failure. For example, if a 250-kcmil conductor is tapped from a set of two 500-kcmil conductors in parallel, the splicing device must include both 500-kcmil conductors and the single 250-kcmil tap conductor.
Greg Fretwell
|
|
|
|
|
Joined: Jul 2007
Posts: 1,337
Member
|
I stand corrected! I missed it was a parallel run of 600's. Excuse me why I sit here looking stupid and eat my crow sandwich...
"Live Awesome!" - Kevin Carosa
|
|
|
|
|
Joined: Jul 2004
Posts: 10,051 Likes: 39
Member
|
It is not insurmountable, you just need a big, 7 hole, Polaris connector.
Greg Fretwell
|
|
|
|
|
Joined: Jul 2007
Posts: 1,337
Member
|
Split bolts mastic pads and Super 88 will do the trick....  Lol!
"Live Awesome!" - Kevin Carosa
|
|
|
|
|
Joined: Jul 2004
Posts: 136
OP
Member
|
It is not insurmountable, you just need a big, 7 hole, Polaris connector. If the feeder is for a transformer, would it be easier to connect (the tap) to the transformer primary connections.
|
|
|
Posts: 4,294