Transformer rating #210167
05/31/13 10:14 AM
05/31/13 10:14 AM
C
cgw  Offline OP
Member
Joined: Jul 2004
Posts: 134
Rochester NY
1. When the NEC refers to a Class 155 transfomer is that the same as a manufacturer's temeperature rise?

2. When the NEC requires that the transformer be installed in a transformer room does that mean a separate room from the electric switchgear and other mechanicals?

2017 / 2014 NEC & Related Books and Study Guides
Re: Transformer rating [Re: cgw] #210169
05/31/13 05:23 PM
05/31/13 05:23 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 977
Chicago Illinois USA
1. No. The temperature rise is stated as the maximum temperature rise above the room ambient. I think what you are referring to as 'Class 155' is a rating of the temperature at which the insulation system fails and the transformer becomes a giant flash bulb.
2. Yes and No. It needs to be in a room separate from things that are not directly associated with the electrical system. That means no chillers, fans, pumps, phone equipment, etc.


Ghost307
Re: Transformer rating [Re: cgw] #210194
06/02/13 06:32 PM
06/02/13 06:32 PM
C
cgw  Offline OP
Member
Joined: Jul 2004
Posts: 134
Rochester NY
Thanks
(I figured 1. out right after I posted)
Is your typical low voltage (say 480X208/120) dry type transformer considered totally enclosed except for the ventilating openings?

Re: Transformer rating [Re: cgw] #210201
06/02/13 10:17 PM
06/02/13 10:17 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,089
Brick, NJ USA
The term 'totally enclosed' does not specifically appear in Art. 100 or 450 (2011 NEC)

Mention is made within 450.21
"450.21 Dry-Type Transformers Installed Indoors.
(A) Not over 1121⁄2 kVA. Dry-type transformers installed
indoors and rated 1121⁄2 kVA or less shall have a separation
of at least 300 mm (12 in.) from combustible material unless
separated from the combustible material by a fireresistant,
heat-insulated barrier.
Exception: This rule shall not apply to transformers rated
for 600 volts, nominal, or less that are completely enclosed, with or without ventilating openings.
(B) Over 1121⁄2 kVA. Individual dry-type transformers of
more than 1121⁄2 kVA rating shall be installed in a transformer room of fire-resistant construction. Unless specified otherwise in this article, the term fire resistant means a construction having a minimum fire rating of 1 hour.
Exception No. 1: Transformers with Class 155 or higher
insulation systems and separated from combustible material
by a fire-resistant, heat-insulating barrier or by not less
than 1.83 m (6 ft) horizontally and 3.7 m (12 ft) vertically.
Exception No. 2: Transformers with Class 155 or higher
insulation systems and completely enclosed except for ventilating openings."

IMHO, a basic 480/120-208 transformer is 'enclosed' by def.; and 'completely' enclosed as the wording within exception 2 above.

A 'totally enclosed' transformer IMHO, is one that is encapsulated and only the pri & sec conductors are visable.


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
255,091 Are you busy
191,195 Re: Forum
180,951 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.9610 MB (Peak: 1.0937 MB) Zlib enabled. Server Time: 2019-05-22 01:12:26 UTC