Manholes #210161 05/30/13 05:40 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
Is there a article in the code that requires a slope of 3% oriented to the manhole? Or does it cover that at all?

Please quote article if possible.

Thank you.

Greg


Don't drive and TEXT! Drive now TALK LATER!
2017 / 2014 NEC & Related Books and Study Guides
Re: Manholes [Re: akmaster] #210163 05/30/13 05:58 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
I believe article 310 covers manholes..


Don't drive and TEXT! Drive now TALK LATER!
Re: Manholes [Re: akmaster] #210173 05/31/13 08:03 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Is the manhole owned by a utility company or privately owned? Is this a service wire, feeder wire from 1 building to another? Maybe the guys need a little more info.

Re: Manholes [Re: akmaster] #210175 05/31/13 08:20 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
It is one of many manholes on an ethanol project...it will contain Medium voltage cables (4160) fiber and control and DC circuits..the are 8'x 8'x8'. They have a base and a top...
the specs call for a 0.3% slope TOWARDS the manhole..

I did not find that requirement anywhere in the code..

It seems they will need racks inside to rack the cables as well..

Thanks,
Greg


Don't drive and TEXT! Drive now TALK LATER!
Re: Manholes [Re: akmaster] #210176 05/31/13 09:24 PM
Joined: Jul 2004
Posts: 9,575
G
gfretwell Offline
Member
Toward the manhole? Is this also the storm drain system?


Greg Fretwell
Re: Manholes [Re: akmaster] #210182 06/01/13 02:36 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Greg,


Check sec. 110 V of the NEC, that talks about manholes and their construction also sec. 490 talks about voltage over 600. You also might have to refer to the National Safety Code. Most utilities follow those rules. I might have an old NESC book around, I would have to look.

Re: Manholes [Re: akmaster] #210186 06/01/13 04:39 PM
Joined: Apr 2002
Posts: 7,237
HotLine1 Offline
Member
This may say something: From '08 Handbook:

"110.70 General.
Electrical enclosures intended for personnel entry and specifically fabricated for this purpose shall be of sufficient size to provide safe work space about electrical equipment with live parts that is likely to require examination, adjustment, servicing, or maintenance while energized. Such enclosures shall have sufficient size to permit ready installation or withdrawal of the conductors employed without damage to the conductors or to their insulation. They shall comply with the provisions of this part.
Exception: Where electrical enclosures covered by Part V of this article are part of an industrial wiring system operating under conditions of maintenance and supervision that ensure that only qualified persons monitor and supervise the system, they shall be permitted to be designed and installed in accordance with appropriate engineering practice. If required by the authority having jurisdiction, design" (documentation may be required)

Last edited by HotLine1; 06/01/13 04:41 PM. Reason: added text in parenthesis

John
Re: Manholes [Re: akmaster] #210208 06/03/13 02:17 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
Thanks for the replies. @ Greg...yes towards the manhole...

@hotline...thanks I will take a look...

I can not find any requirement regarding slope of 0.3 percent towards the manhole for conduits...

does this include the whole run from man hole to man hole?

regards

Greg


Don't drive and TEXT! Drive now TALK LATER!
Re: Manholes [Re: akmaster] #210230 06/04/13 02:15 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
Another question: Is it not a requirement that manholes with high voltage are required to have the cover labeled "DANGER HIGH VOLTAGE"?

Thanks

GW

Last edited by akmaster; 06/04/13 02:15 PM.

Don't drive and TEXT! Drive now TALK LATER!
Re: Manholes [Re: akmaster] #210231 06/04/13 02:25 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
One more...Does the Manhole cover have to be grounded?


Don't drive and TEXT! Drive now TALK LATER!
Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
BigB 1
Popular Topics(Views)
277,576 Are you busy
211,251 Re: Forum
198,275 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3