Portable Generator Grounding #209923
05/14/13 06:46 PM
05/14/13 06:46 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
Any portable generator that is hard wired to equipment or devices must be grounded to earth as I understand OSHA. If there are cord and plug connections then no ground rod is required. Is this correct?

Thanks

Greg

Last edited by akmaster; 05/14/13 06:46 PM.

Don't drive and TEXT! Drive now TALK LATER!
2017 / 2014 NEC & Related Books and Study Guides
Re: Portable Generator Grounding [Re: akmaster] #209925
05/14/13 08:12 PM
05/14/13 08:12 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
A 'cord & plug' connection is the 'EGC' (equipment grounding conductor) It is not a GEC, nor a Bond.

The earth ground for a 'portable' (3-8+/-KW) is a much debated topic and common practice is to just run it.



John
Re: Portable Generator Grounding [Re: akmaster] #209926
05/14/13 08:39 PM
05/14/13 08:39 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
I have always questioned why you would even want to ground a truly portable generator (cord loads only).
There is a modicum of safety in having the generator ungrounded. With no ground reference, there is no danger from a fault to ground.


Greg Fretwell
Re: Portable Generator Grounding [Re: akmaster] #209928
05/14/13 09:22 PM
05/14/13 09:22 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
gfretwell:

I had this debate as an EC back in '05 regarding portable light towers. Diesel, 4-6 1000 watt MH floods, and 2-120 volt GFIs on board. (Towable units)

The AHJ wanted grd rods at each unit. I had 65 units spread out over grass, paved parking lots, quarry auxilary parking & a few municipal streets.

Discussions, and a polite request for an article number eliminated the rods.



John
Re: Portable Generator Grounding [Re: akmaster] #209929
05/14/13 10:45 PM
05/14/13 10:45 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
There are a lot of small generators that do not bond the neutral, most notably the Honda inverters.
This really only becomes an issue if you try to hook one to a 3 wire transfer switch.

I lifted the bond on my 5.5KW genset because my plan is to connect it with my breaker interlock. I already have the pigtail mounted on the side of the house for it. So far we have not had an outage worth filling it with gas.
(2 years for me and 3 years for the guy I bought it from)
My UPS's carried me through the last one. It was funny sitting there with both PCs running and the TV, satellite etc still going. If the kitchen light had not gone off I might not have even noticed.



Greg Fretwell
Re: Portable Generator Grounding [Re: akmaster] #209932
05/15/13 10:31 AM
05/15/13 10:31 AM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
OSHA says that any hard wired cord connected supply from the generator has to have a ground rod bonded to the frame of the generator. If you have cord and plug connected only, no ground rod is required.

Here is the article:

http://click.infospace.com/ClickHandler.ashx?du=www.osha.gov%2f...%2fgrounding_port_generator.pdf&ru=http%3a%2f%2fwww.osha.gov%2fOshDoc%2fdata_Hurricane_Facts%2fgrounding_port_generator.pdf&ld=20130515&ap=1&app=1&c=snapdov3a.5&s=snapdov3a&coi=771&cop=main-title&euip=70.195.4.96&npp=1&p=0&pp=0&pvaid=6d1c792782f74931a5905afa937d6da7&ep=1&mid=9&hash=A1E9D9E485178B3B64C4E759ABAE3F08

Thank you,

Greg


Don't drive and TEXT! Drive now TALK LATER!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28